Results 1 to 8 of 8
    pacman's Avatar
    pacman Guest
    Angry 01 fault on fujitsu
    i,m having trouble with a 01 fault on a fujitsu split model aoy54 there was a power surge which blew the filter board on the evap & it also blew the inverter board on condensor i have replaced both boards the system ran for a while then the same 01 fault was brought back up any suggestions please
    Jan 2003
    East Anglia
    1,160
    Re: 01 fault on fujitsu
    pacman,
    01 on most things is a communications fault but not sure on this, try
    www.oceanair.uk.com/pages/technical
    may be something on there
    Raymond
    Oct 2001
    Nottingham UK
    5,668
    If you can pick up the 2006/2007 Air Conditioning catalogue from NRS (Climate Centre) you will find all the fault codes for Fujitsu, Panasonic and others in the back pages.
    Sep 2005
    33
    Quote Originally Posted by pacman View Post
    Hi Mate
    You sound as if you need to ring Hatem at Fujitsu technical support on 07748966312. He's very good & has always helped me out.
    Best regards
    Frostycold
    Split Croatia
    57
    6,151
    36
    This is troubleshooting chart for that error.
    Apr 2006
    stafford
    42
    974
    http://www.climatecenter.co.uk/climt/index.html
    a link to download the above book,very helpfull
    Paul
    "KEEP IT COOL"
    Jul 2007
    Australia
    1,845
    o1 error is comms error between indoor and outdoor unit.
    disconnect the serial comms wir at the outdoor unit, making sure its safe and out of the way when you turn it back on.
    Check the voltage on the #3 terminal (still wired up to the indoor) check the voltage at the wire you removed (which is connected to the outdoor pcb)
    you should get 90-120v ac from either, whatever one has no/low voltage is dead.
    might be the control board itself, or a board that supplies power the the control board.
    My bet is if you had a power surge, possibly more that just the indoor filter PCB and outdoor inveter PCB would be blown too.
    I.e there's a outdoor filter pCB and a indoor control PCB.
    What does the indoor unit do, is there display on the controller, does the indoor fan turn on when on fan mode?
    edit: What does the outdoor unit do, when you first turn it on via the isolator does the power relay click in, do you hear the tx valve hammer open/closed for 5 seconds?
    Nov 2007
    go fujitsugeneral.com
    contractor login
    User-name instuller
    password 1ton12kbtu
  1. lg fridge/freezer fault light on function display board
    By bazza in forum Trouble Shooting
    Last Post: 25-02-2007, 03:25 PM
  2. u4 fault on a Daikin inverter
    By phil17 in forum Air Conditioning
    Last Post: 05-02-2007, 02:41 AM
  3. Chiller fault
    By iceman007 in forum Trouble Shooting
    Last Post: 27-06-2006, 06:15 AM
  4. Fujitsu AOT24PMAL Fault Codes
    By johnmart in forum Trouble Shooting
    Last Post: 19-04-2004, 06:39 AM