Results 1 to 8 of 8
  1. #1
    pacman's Avatar
    pacman Guest

    Angry 01 fault on fujitsu



    i,m having trouble with a 01 fault on a fujitsu split model aoy54 there was a power surge which blew the filter board on the evap & it also blew the inverter board on condensor i have replaced both boards the system ran for a while then the same 01 fault was brought back up any suggestions please



  2. #2
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: 01 fault on fujitsu

    pacman,

    01 on most things is a communications fault but not sure on this, try
    www.oceanair.uk.com/pages/technical

    may be something on there

    Regards

    Raymond

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: 01 fault on fujitsu

    If you can pick up the 2006/2007 Air Conditioning catalogue from NRS (Climate Centre) you will find all the fault codes for Fujitsu, Panasonic and others in the back pages.

  4. #4
    Join Date
    Sep 2005
    Location
    UK
    Posts
    33
    Rep Power
    0

    Re: 01 fault on fujitsu

    Quote Originally Posted by pacman View Post
    i,m having trouble with a 01 fault on a fujitsu split model aoy54 there was a power surge which blew the filter board on the evap & it also blew the inverter board on condensor i have replaced both boards the system ran for a while then the same 01 fault was brought back up any suggestions please
    Hi Mate
    You sound as if you need to ring Hatem at Fujitsu technical support on 07748966312. He's very good & has always helped me out.

    Best regards
    Frostycold

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: 01 fault on fujitsu

    This is troubleshooting chart for that error.
    Last edited by nike123; 13-12-2007 at 11:53 AM.

  6. #6
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    19

    Re: 01 fault on fujitsu

    Quote Originally Posted by frank View Post
    If you can pick up the 2006/2007 Air Conditioning catalogue from NRS (Climate Centre) you will find all the fault codes for Fujitsu, Panasonic and others in the back pages.

    http://www.climatecenter.co.uk/climt/index.html

    a link to download the above book,very helpfull
    Paul


    "KEEP IT COOL"

  7. #7
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: 01 fault on fujitsu

    o1 error is comms error between indoor and outdoor unit.
    disconnect the serial comms wir at the outdoor unit, making sure its safe and out of the way when you turn it back on.
    Check the voltage on the #3 terminal (still wired up to the indoor) check the voltage at the wire you removed (which is connected to the outdoor pcb)
    you should get 90-120v ac from either, whatever one has no/low voltage is dead.
    might be the control board itself, or a board that supplies power the the control board.
    My bet is if you had a power surge, possibly more that just the indoor filter PCB and outdoor inveter PCB would be blown too.
    I.e there's a outdoor filter pCB and a indoor control PCB.
    What does the indoor unit do, is there display on the controller, does the indoor fan turn on when on fan mode?
    edit: What does the outdoor unit do, when you first turn it on via the isolator does the power relay click in, do you hear the tx valve hammer open/closed for 5 seconds?
    Last edited by paul_h; 07-10-2007 at 01:51 PM.

  8. #8
    Join Date
    Nov 2007
    Location
    USA
    Posts
    17
    Rep Power
    0

    Re: 01 fault on fujitsu

    go fujitsugeneral.com
    contractor login
    User-name instuller
    password 1ton12kbtu

Similar Threads

  1. lg fridge/freezer fault light on function display board
    By bazza in forum Trouble Shooting
    Replies: 0
    Last Post: 25-02-2007, 03:25 PM
  2. u4 fault on a Daikin inverter
    By phil17 in forum Air Conditioning
    Replies: 39
    Last Post: 05-02-2007, 02:41 AM
  3. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  4. Fujitsu AOT24PMAL Fault Codes
    By johnmart in forum Trouble Shooting
    Replies: 5
    Last Post: 19-04-2004, 06:39 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •