Results 1 to 17 of 17
Thread: Daikin Hard wired controller
Hybrid View
-
21-05-2007, 05:43 PM #1
Daikin Hard wired controller
Been on the daikin commisioning installlation and service course today. Spoke to the trainer about how to use the controller to look at the readings from the thermisters but i only managed to get the outdoor thermister readings (if that makes sense). I got it off going to 40 on the hardwired controller. Does anyone have a list of the codes that would be useful when at the controller such as the indoor thermisters as well because i figure that if i have them all then you would be able to look at the superheat and subcooling through the controller and what everelse is relevant...
-
21-05-2007, 06:13 PM #2
Re: Daikin Hard wired controller
Go to the Daikin website and download the Sky Air tech book - ESIE03-01SkyAir L.pdf
You'll find most things in there.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
21-05-2007, 06:33 PM #3
Re: Daikin Hard wired controller
Ok thanks brian..
-
21-05-2007, 06:46 PM #4
Re: Daikin Hard wired controller
Hello Marc
To make a complete control you need a small controler called RSUK919: it's a mini-checker that read data between indoor and outdoor units for split/multi/sky air from r22 to r410a heat pump series...
Maybe you can order it from your local supplier ?
As far as i know you can only read indoor temperature through the wired remote...
Regards
cool#9
-
21-05-2007, 07:31 PM #5
-
21-05-2007, 07:53 PM #6
Re: Daikin Hard wired controller
Am i the first one to speak about this device ?
Well it's simple you just plug on 1/2/3 terminals and check either indoor or outdoor unit. No battery is needed. There are two ways to connect; 1 for r22/r407c series and 1 for r410a depending on the power supply (1/3 or 1/2).
You can also connect it to a bigger checker via a little interface and helped by a sofware to do recording, monitoring for harder diagnosis...
See the picture !
Regards
cool#9Last edited by cool#9; 09-10-2007 at 05:16 PM.
-
21-05-2007, 09:32 PM #7
Re: Daikin Hard wired controller
were else can you buy thos analyzers from any suggestions guy thanks alot
-
24-05-2007, 11:27 PM #8
Re: Daikin Hard wired controller
Hey cool9, I didnt even know the RSUK919 existed...!! nice one.
Think its time to have a word with our supplier and invest in these for our service team, we already have the inverter checkers though.
Similar Threads
-
Daikin not working... many problems
By stankovicv in forum Air ConditioningReplies: 26Last Post: 11-12-2010, 09:01 AM -
Electronic controller probes wired wrong
By Electrocoolman in forum Trouble ShootingReplies: 3Last Post: 12-11-2007, 06:39 PM -
daikin remote controller setting list
By knight rider in forum Air ConditioningReplies: 9Last Post: 21-05-2007, 10:10 PM -
daikin controller pdf
By rbartlett in forum Air ConditioningReplies: 9Last Post: 29-12-2006, 06:39 AM -
Daikin controller question
By THERMOACC in forum Air ConditioningReplies: 9Last Post: 10-03-2006, 10:48 PM