    Leave some form of acess to the suction side. Take off the schraders and use "hand valves", not ball valves.

    Most anybody with refrigeration experience can get a cascade to work, No disrespect intended to anyone. The trick is to increase the longevity of the system.

    the factory cascades that i repair have an average life span of 8 years +. Our rebuilds on the same units have a life expectancy of 5 + years. The temps and the equipment are unforgiving and it all comes down to the details in the process.

    Your worst enemy is moisture in the system. Your best freind is vacuum and dry nitrogen. Try to achive a vacuum of less than 100 microns/millitorr. You should be able to blank off and remaine under 400 microns for 30 minutes. Get rid of the charging hoses and and use copper line from the manifold to the unit and to the vacuum pump. Charging hoses wil not let you achieve a deep vacuum because of the material they are made of, they constantly off gas.

    Your kung fu looks good, Now lets make it last.
    Last edited by ultralo1; 18-05-2007 at 04:01 AM. Reason: some stupid spelling

  2. #2
    Join Date
    Nov 2006
    Location
    Essex
    Age
    40
    Posts
    49
    Rep Power
    0

    Re: My First Cascade "Fat Boy"

    My cascade running "Download a free user"
    http://rapidshare.com/files/29054309...ge_running.AVI

    It hasnt any mounts on the bottom of the cascade. It did sound nice when run but now a little nosiey?

    I know i did a wrong move with the HX not being capped off. Wont do it again. I vacuumed it for a few ohs and blasted through with nitrogen to be sure.

    Does the compressor sound nackard then chilling out?

  3. #3
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: My First Cascade "Fat Boy"

    Yes, it does.

    Think of a motor spinning round inside held in place with 3 springs, now remove a spring and the motor falls to one side and rattles against the casing.
    Someone might have a picture for you to see.

    Did you drop the comp at any time?

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  4. #4
    Join Date
    Nov 2006
    Location
    Essex
    Age
    40
    Posts
    49
    Rep Power
    0

    Re: My First Cascade "Fat Boy"

    Did you drop the comp at any time?

    No mate, was sounding sweet as a nut then i fixed it all together with the build and now it sounds a little doggy to say the least.

    Its working correct as in temps and pressures. Whats the downfall regards running it if it is as you mentioned?

  5. #5
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: My First Cascade "Fat Boy"

    Whats the downfall regards running it if it is as you mentioned?
    Well you already know about the noise...lol

    Eventually the internal pipes will rupture and render the comp useless.

    Any chance of sending it back?

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  6. #6
    Join Date
    Nov 2006
    Location
    Essex
    Age
    40
    Posts
    49
    Rep Power
    0

    Re: My First Cascade "Fat Boy"

    Quote Originally Posted by chillin out View Post
    Well you already know about the noise...lol

    Eventually the internal pipes will rupture and render the comp useless.

    Any chance of sending it back?

    Chillin
    No mate, i got it from a air con unit that was office clearance. I got it along with the other unit that is fine.

    Dam man, gutted to say the least. I don't suppose anyone has a compressor that kind of power floating about.

    Just when i was ready to complete the 2nd stage this weekend.

  7. #7
    Join Date
    Nov 2006
    Location
    Essex
    Age
    40
    Posts
    49
    Rep Power
    0

    Re: My First Cascade "Fat Boy"

    chillin out
    I thought i would mention. When the compressor was fired up without any refrigerant inside it run quite and nice and smooth.

    However now its very loud as you know from the video. Could this be due to the pressure in the first stage? 90PSI Static 200PSI Running IDLE?

    When i claim some refrigerant back which lowers the pressure it sounds a bit better.

    I am just trying to convince myself its not focked

Similar Threads

  1. Cascade Refrigeration System
    By Vincent Yu in forum Fundamentals
    Replies: 71
    Last Post: 16-02-2012, 04:04 AM
  2. R-23 cascade system
    By S.M.Gokhale in forum Industrial
    Replies: 22
    Last Post: 08-08-2009, 08:04 AM
  3. Refrigerant for multi-stage and cascade systems
    By lraja in forum Refrigerants
    Replies: 0
    Last Post: 15-01-2007, 01:27 AM
  4. cascade systems
    By Nuklhed in forum Refrigeration Books
    Replies: 5
    Last Post: 30-03-2006, 01:04 PM
  5. Regulation regarding hydrocarbons in an cascade
    By DaBit in forum Fundamentals
    Replies: 4
    Last Post: 19-01-2004, 12:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •