    ammonia liquid



    Hello guys

    How r u?

    I have question for the ammonia liquid with low temp. and pumping with the ammonia pump. It is possible if the velocity of liquid ammonia with low temp we increase will be build up the gas?

    many thanks



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: ammonia liquid

    When you pump liquid ammonia the pressure increase generates subcooling. You can see this on a pressure-enthalpy diagram.

    The extent of pressure increase created by the pump means you can increase the friciton losses or static head losses equal to the pressure added by the pump, before the liquid will flash off into a vapor.
    If all else fails, ask for help.


  3. #3
    Join Date
    Mar 2007
    Location
    jakarta
    Age
    49
    Posts
    30
    Rep Power
    0

    Re: ammonia liquid

    Now I have a problem with ammonia liquid pump is sometimes cavitation (at low pressure receiver -40degC). I have check the pump is over capacity so they have make adjusment and decrease the pipe suction and discharge sizing. My suspect is if they make sizing down for that pipe the velocity become increase and flash in to the vapor like u said, its correct?

    thanks for your help

  4. #4
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: ammonia liquid

    Dear US Iceman,

    By any chance can you put up the PH diagram for this pump pressure increase & the Superheat increase point.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: ammonia liquid

    Smpsmap, this is a normal log/p for NH3 where you have to plot the real cycle on it.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: ammonia liquid

    Quote Originally Posted by faryuki
    Now I have a problem with ammonia liquid pump is sometimes cavitation (at low pressure Receiver -40degC). I have check the pump is over capacity so they have make adjusment and decrease the pipe suction and discharge sizing.
    Reducing the pipe size will not help. If the pump is a centrifugal pump, you can decrease the flow rate of the ppump by partially closing the pump discharge valve. This forces the pump to operate at a lower flow rate by increasing the pump discharge pressure.

    If the pump is trying to pump too much liquid, the NPSHR (net positive suciton head required by the pump) can increase dramatically, which causes the pump to cavitate.

    That's only one possible explanation. but it is the most likely.
    If all else fails, ask for help.


Similar Threads

  1. liquid ammonia pump calvitation
    By Kathleen in forum Trouble Shooting
    Replies: 23
    Last Post: 20-05-2011, 02:18 AM
  2. Ammonia liquid pump
    By jessica in forum NH3
    Replies: 19
    Last Post: 30-05-2008, 12:53 PM
  3. Liquid ammonia injection for cooling.
    By mrsparky in forum Industrial
    Replies: 91
    Last Post: 19-04-2007, 09:44 PM
  4. Ammonia Liquid Pumps
    By nh3wizard in forum NH3
    Replies: 8
    Last Post: 05-09-2006, 07:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •