    Apologies for asking what is probably a very simple question but I'm a first year apprentice still trying to get my head around this trade . Anyway, was wondering if a system is severly overcharged, what are the ramifications? Does it mean that the evaporator temp is too high and does it put any of the other componenets under stress? Can I also ask the same question but for a system that is undercharged? Thanks in advance for any advice given



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,645
    Rep Power
    23

    Re: Charging the system

    Over charge over works the compressor and shortens life time, under charge system cycles are shorter over working thermistat contacts and stressing compressor yet again shortening its life.

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Charging the system

    TEV or capillary system?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    894
    Rep Power
    19

    Re: Charging the system

    Hi Colin,

    Quote Originally Posted by Colin Gray View Post
    Apologies for asking what is probably a very simple question but I'm a first year apprentice still trying to get my head around this trade . Anyway, was wondering if a system is severly overcharged, what are the ramifications? Does it mean that the evaporator temp is too high and does it put any of the other componenets under stress? Can I also ask the same question but for a system that is undercharged? Thanks in advance for any advice given
    If Overcharged :
    1-Suction pressure High (i.e. , evaporating temperature High)
    2- Discharge pressure High (i.e. , condensing temperature High)
    3- Super heat Low for cap tube system. If TEV is used then it depends on the amount of overcharge. If the system is too much charged then super heat would be Low.
    4- Sub cooling high

    If Undercharged :
    1-Suction pressure Low (i.e. , evaporating temperature Low)
    2- Discharge pressure Low (i.e. , condensing temperature Low)
    3- Super heat High
    4- Sub cooling Low

    Be careful : If there is non-condensibles present then you will have the exact symptoms of "Overcharged" fault. The only way to distinguish between them is to do "Non-Condensibles" Test.

    If evaporating temperature goes up (I mean more than the design value), then cooling capacity decreases. Also, this means that the compressor amp will go up. All depends on the amount of increase or decrease really.

    Hope this helps.
    Cheers
    Last edited by lana; 13-05-2007 at 06:20 AM.
    Even Einstein Asked Questions

  5. #5
    Join Date
    Mar 2007
    Location
    Northern Ireland
    Age
    36
    Posts
    42
    Rep Power
    0

    Re: Charging the system

    Quote Originally Posted by lana View Post
    Hi Colin,



    Be careful : If there is non-condensibles present then you will have the exact symptoms of "Overcharged" fault. The only way to distinguish between them is to do "Non-Condensibles" Test.

    If evaporating temperature goes up (I mean more than the design value), then cooling capacity decreases. Also, this means that the compressor amp will go up. All depends on the amount of increase or decrease really.

    Hope this helps.
    Cheers
    What do you mean by the non-condensibles test?

  6. #6
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    894
    Rep Power
    19

    Re: Charging the system

    Hi to you too,
    Please read the link below :
    Its Post #5.

    http://www.refrigeration-engineer.co...ht=condensible


    Cheers
    Even Einstein Asked Questions

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 11:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  4. Charging a system
    By shark26 in forum Fundamentals
    Replies: 32
    Last Post: 31-01-2006, 07:41 PM
  5. System charging
    By Dylan in forum Fundamentals
    Replies: 10
    Last Post: 17-12-2004, 11:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •