Thread: Charging the system
-
12-05-2007, 06:43 PM #1
Charging the system
Apologies for asking what is probably a very simple question but I'm a first year apprentice still trying to get my head around this trade . Anyway, was wondering if a system is severly overcharged, what are the ramifications? Does it mean that the evaporator temp is too high and does it put any of the other componenets under stress? Can I also ask the same question but for a system that is undercharged? Thanks in advance for any advice given
-
12-05-2007, 06:49 PM #2
Re: Charging the system
Over charge over works the compressor and shortens life time, under charge system cycles are shorter over working thermistat contacts and stressing compressor yet again shortening its life.
-
12-05-2007, 09:14 PM #3
Re: Charging the system
TEV or capillary system?
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
13-05-2007, 06:16 AM #4
Re: Charging the system
Hi Colin,
If Overcharged :
1-Suction pressure High (i.e. , evaporating temperature High)
2- Discharge pressure High (i.e. , condensing temperature High)
3- Super heat Low for cap tube system. If TEV is used then it depends on the amount of overcharge. If the system is too much charged then super heat would be Low.
4- Sub cooling high
If Undercharged :
1-Suction pressure Low (i.e. , evaporating temperature Low)
2- Discharge pressure Low (i.e. , condensing temperature Low)
3- Super heat High
4- Sub cooling Low
Be careful : If there is non-condensibles present then you will have the exact symptoms of "Overcharged" fault. The only way to distinguish between them is to do "Non-Condensibles" Test.
If evaporating temperature goes up (I mean more than the design value), then cooling capacity decreases. Also, this means that the compressor amp will go up. All depends on the amount of increase or decrease really.
Hope this helps.
CheersLast edited by lana; 13-05-2007 at 06:20 AM.
Even Einstein Asked Questions
-
13-05-2007, 12:21 PM #5
-
13-05-2007, 02:47 PM #6
Re: Charging the system
Hi to you too,
Please read the link below :
Its Post #5.
http://www.refrigeration-engineer.co...ht=condensible
CheersEven Einstein Asked Questions
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
System Burn Out Troubleshooting
By altaf22m in forum Technical DiscussionsReplies: 13Last Post: 07-05-2010, 09:24 AM -
Burn out System, Clean up procedure. & Troubleshooting.
By altaf22m in forum CommercialReplies: 19Last Post: 15-04-2008, 07:03 PM -
Charging a system
By shark26 in forum FundamentalsReplies: 32Last Post: 31-01-2006, 06:41 PM -
System charging
By Dylan in forum FundamentalsReplies: 10Last Post: 17-12-2004, 10:37 PM