    chosing the right evaporator



    Can someone please tell me the difference betwwen flooded and non - flooded shell and tube type evaporators; based on capacity, condition of the vapur leaving the evaporator, heat transfer effectiveness, construction and control.

    Thank you in advance



  2. #2
    Join Date
    Mar 2005
    Location
    Nearby
    Age
    51
    Posts
    22
    Rep Power
    0

    Re: chosing the right evaporator

    In flooded type u have a shell semi-full of refrigerant like a pool and the compressor sucks from this shell (no expansion valve)but in tube type as the name implies liquid evaporates inside the tubes.
    To best of my knowledge in large capacities flooded type in prefered

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: chosing the right evaporator

    Shell & tube heat exchangers:

    Flooded - this means the refrigerant is on the outside of the tubes and inside of the shell (usually called the shell-side of the heat exchanger). The refrigerant exit condition is a saturated vapor.

    Heat transfer is by pool boiling or nucleation. The liquid boils around the tubes and the vapor generated travels upwards and back to the compressor(s).

    Direct Expansion - this means the refrigerant is expanding inside of the tube (usually called the tube-side of the heat exchanger). The refrigerant exit condition is a superheated vapor if the TXV is set and controlling properly.

    Heat transfer is by forced convection boiling. As the liquid evaporates less liquid is available. Therefore the vapor condition is continually increasing at a saturated condition, until all of the liquid is evaporated. Superheating of the vapor then occurs.
    If all else fails, ask for help.


  4. #4
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: chosing the right evaporator

    As a point to note, the flooded chillers have a a thermal expansion valve. You have to have some point of expansion and on a flooded chilller it is ether a control valve controlled by the level on the chiller (low side control) or a high side level control located at the condenser/receiver. With a high side float, you can have wither a critical charge system or a non-critical charge system.

    DX control uses a thermal control vlave for expansion. This is valve is normally either a filled capilliary type witha filled charge in the bulb, or an electronic stepper type valve. You can also either feed the liquid through capilliary tubes and distributor or just an orifice.

    As US Iceman explainted the flooded has thetubes on the shell. You can also use a thermo siphon design which is a flooed desigh, but the tubes are on the refrigerant side.

    Now if you are talking about unit coolers, you can have a flooded design that has the coil tubes fed by a thermisiphom drum. Some people also refer to a pumped recirculation or over-feeddesign as flooded.

    Isn't referation a wonder thing. When we have so many ways to describe the saame thing.

    Ken

  5. #5
    Join Date
    Apr 2007
    Location
    london
    Posts
    6
    Rep Power
    0

    Re: chosing the right evaporator

    whats the best refrigerant for perishable application

  6. #6
    Join Date
    Jan 2007
    Location
    China
    Posts
    9
    Rep Power
    0

    Re: chosing the right evaporator

    I think the flooded evaporator is better for big capacity personally,but there is another problem of refrigerant charge,too much refrigerant charge sometimes influence the evaporating temperature,for small scale capacity unit,dry evaporator is better.

  7. #7
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: chosing the right evaporator

    Best refrigerant depends on size of the unit as well as the temperature. If the system is small enough, I would use a DX and probably R507. I don't like to use the 400 series as they are all blends where 507 is an azetrope. If it is a cooler application, look at R-134A.

    For larger plants, look at pumped recirculator systems on ammonia.

    My 2 cents worth.

    Ken

Similar Threads

  1. Designing Roll Bond Evaporator
    By Munzar Ata in forum Fundamentals
    Replies: 11
    Last Post: 05-08-2010, 11:31 AM
  2. What is the best location for a evaporator fan?
    By Jasno999 in forum Fundamentals
    Replies: 3
    Last Post: 21-02-2007, 12:34 AM
  3. Replies: 3
    Last Post: 06-11-2006, 05:04 AM
  4. Change evaporator
    By tralex in forum Fundamentals
    Replies: 6
    Last Post: 29-12-2005, 07:53 PM
  5. refrigerant velocity in evaporator
    By BESC5240 in forum Trouble Shooting
    Replies: 54
    Last Post: 11-07-2005, 12:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •