Results 1 to 4 of 4
  1. #1
    Join Date
    Nov 2005
    Location
    Liverpool
    Age
    49
    Posts
    56
    Rep Power
    19

    PIR Control for a Daikin



    Gents... Our place is beconing very focused on energy usage. To keep them happy, I've recently been insatlling Daikin FTXS hi-walls with the built-in occupancy sensor. This prevents the units running on full power when the room is unoccupied... thus saving some energy.
    A high-wall is unsuitable for the latest application so I'm looking at an under-ceiling 4-way blow cassette. (An FUQ125).
    This unit ticks all the boxes except for infra-red control. Does anyone have any ideas on how to stop the unit being left on full blast when the room is un occupied/over the weekend etc. The people who use the room can't be relied on. The unit will be stand-alone. Can PIR control be incorporated... or is there another way?
    Thanks in anticipation! DM



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: PIR Control for a Daikin

    You can use a KRP41 pcb with the FUQ125 and control the indoor temperature by wiring a variable resistor or fixed resistor across terminals A+ & A-.

    You could use the relay outputs of a PIR to achieve this, having the PIR contacts N/O during occupied times and the BRC1B controller then allowing set point to be selected and with the PIR contacts closed during un-occupied times the fixed or variable resistor setting the room temp.

    What room temp were you thinking of when the room is un-occupied? Or would it be simpler to allow the PIR to switch the unit off altogether? This can be achieved with the same KRP board.

  3. #3
    Join Date
    Jan 2007
    Location
    SPAIN
    Posts
    172
    Rep Power
    18

    Re: PIR Control for a Daikin

    The concept of PIR control is attractive and sensible, but how many customers understand that you must put this setting to ON with the FTXS units?

    I note that Mitsubishi Electric has a PIR controlled A/C that also targets hot areas - any reports on how this is working?

  4. #4
    Join Date
    Nov 2005
    Location
    Liverpool
    Age
    49
    Posts
    56
    Rep Power
    19

    Re: PIR Control for a Daikin

    Yes momo, you'd be suprised (or not suprised, depending on how cynical you are) at how may times I come to a unit which has had the sensor de-activated. It could really do with some password protection!
    Frank, thanks for your advice. We'll see what "they" say!
    DM

Similar Threads

  1. Daikin vrv control wiring
    By Jase in forum Air Conditioning
    Replies: 4
    Last Post: 23-03-2011, 04:01 AM
  2. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  3. Replies: 21
    Last Post: 05-07-2008, 10:48 AM
  4. Control scenario
    By Mike Hopkins in forum Technical Discussions
    Replies: 5
    Last Post: 14-09-2007, 11:25 AM
  5. New Capacity Control Solution
    By embrown in forum New Technologies
    Replies: 19
    Last Post: 30-12-2003, 01:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •