    Superheat for the umpteenth time



    My apologies in advance, shoot me down for being a wally!


    I was trying to set up a new system today and was checking my superheat. The system runs on R22. I took the suction pressure at the evaporter outlet and converted to temperature and i got
    -16 degrees C. I then took the actual pipe temperature after the T.E.V but before the evaporter and got 10 degrees C.

    Now do i subtract 10 from -16 or am i getting this the wrong way round.

    Any help will be much appreciated, and i know this subject has been covered at length already, just need a kick in the right direction.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Superheat for the umpteenth time

    You have to measure temperature at the outlet of your evaporator and subtract.
    Temperature and pressure must be measured on the same place to know SH on that place.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Jul 2008
    Location
    England
    Age
    39
    Posts
    31
    Rep Power
    0

    Re: Superheat for the umpteenth time

    Thanks Peter.

    So im subtracting and looking for a temperature difference of between 4-7?

  4. #4
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Superheat for the umpteenth time

    You are supposed to measure the pipe temp at the same place you take the pressure reading then subtract your temp.(from the pt conversion) from the pipe temp.
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Superheat for the umpteenth time

    Quote Originally Posted by Mish View Post
    My apologies in advance, shoot me down for being a wally!


    I was trying to set up a new system today and was checking my superheat. The system runs on R22. I took the suction pressure at the evaporter outlet and converted to temperature and i got
    -16 degrees C. I then took the actual pipe temperature after the T.E.V but before the evaporter and got 10 degrees C.
    The refrigerant is boiling off at -16C. For it's temperature to rise up to 10C, it must rise 16 degrees to reach zero and then another 10 degrees to reach 10C. It rose a total of 26 degrees. Your superheat is 26K.

  6. #6
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Superheat for the umpteenth time

    I then took the actual pipe temperature after the T.E.V but before the evaporter and got 10 degrees C.
    Sorry Gary but it hasn't had a chance to be superheated by the evap. yet!

    I would gladly send some glasses in exchange for a set of your tech books.
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  7. #7
    Join Date
    Jul 2008
    Location
    England
    Age
    39
    Posts
    31
    Rep Power
    0

    Re: Superheat for the umpteenth time

    Hi Gary i was hoping for a reply from you.
    Yeah thats what i made my SH reading at, 26k. I thought that seen as it was so high it was not the correct reading.
    I understand i am looking for a reading of between 4-7k.
    Iv determined i have the correct charge of refrigerant from taking my subcooling and have achieved a measurement of 3k.
    I have good airflow through condenser and evaporator so just need to tweak SH to get optimum efficiency from my system.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Superheat for the umpteenth time

    Quote Originally Posted by TRASH101 View Post
    Sorry Gary but it hasn't had a chance to be superheated by the evap. yet!

    I would gladly send some glasses in exchange for a set of your tech books.
    Good catch.

    If I had some glasses I might be able to read your second paragraph.

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Superheat for the umpteenth time

    Quote Originally Posted by Mish View Post
    I then took the actual pipe temperature after the T.E.V but before the evaporter...
    As Trash101 correctly pointed out, you are measuring flash gas temp (not superheat) and this tells you absolutely nothing useful.

    Superheat is measured at the outlet of the evaporator.

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Superheat for the umpteenth time

    Just an aside to this thread but how come you are installing a new R22 system ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Superheat for the umpteenth time

    Just an aside to this thread but how come you are installing a new R22 system ?
    Its obviously taken months to install

    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  12. #12
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Superheat for the umpteenth time

    And for pities sake don't tell Multisync
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  13. #13
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Superheat for the umpteenth time

    Mish.
    asper previous, the pipe temp reading is at the thermo buld position.
    To check correct setting first establish the evap TD., air on versus evaporationg pressure converted to temp. Super heat should be 60>70% of that calculation, wait 15 mins if adjusting TEV.
    Example: air on at -5'C evap press/temp -16'C , Evap TD is 11 degrees, by 65% = nominal 7 degrees superheat. Evaporating -16 suction pipe temp should around -9 'C , can be checked during pulldown or at design.

  14. #14
    Join Date
    Jul 2008
    Location
    England
    Age
    39
    Posts
    31
    Rep Power
    0

    Re: Superheat for the umpteenth time

    I have not installed a new R22 system. It was an existing system that wasnt able to cope with a lower temperature we now want to run at.
    The system consisted of 1 compressor and 2 evaporators. I split the system and added a new compressor pack running on R404A.
    The systems now supply 1 evaporator each.

    Thank you all for your help

  15. #15
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: Superheat for the umpteenth time

    Quote Originally Posted by Magoo View Post
    Mish.
    To check correct setting first establish the evap TD., air on versus evaporationg pressure converted to temp. Super heat should be 60>70% of that calculation, wait 15 mins if adjusting TEV.
    Example: air on at -5'C evap press/temp -16'C , Evap TD is 11 degrees, by 65% = nominal 7 degrees superheat. Evaporating -16 suction pipe temp should around -9 'C , can be checked during pulldown or at design.
    Great info mate

Similar Threads

  1. 9 superheat & subcooling scenarios
    By nike123 in forum Fundamentals
    Replies: 39
    Last Post: 19-07-2011, 03:16 AM
  2. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  3. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  4. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  5. superheat
    By scott12 in forum Air Conditioning
    Replies: 9
    Last Post: 19-11-2007, 11:36 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •