    compressor replace



    Hai sirs,
    any body have any experiance about replace of compressor reciprocating and rotary .If i replace compressor reciprocating inplace of rotary have any problem will come at the working time . I have doubt about the capilllary design of reciprocating and rotary systems .Anybody can help me.



  2. #2
    Join Date
    Mar 2007
    Location
    canada
    Age
    43
    Posts
    47
    Rep Power
    0

    Re: compressor replace

    What size of compressor are you replacing and what application?

  3. #3
    Join Date
    Mar 2007
    Location
    uae
    Age
    44
    Posts
    24
    Rep Power
    0

    Re: compressor replace

    Hai good guy
    compressor same LRA, same BTU but changing reciprocating in place of rotary.wall mount type split a/c.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: compressor replace

    If you have the the same cooling capacity and the operating conditions (evaporating and condensing temperature and the same refrigerant), why would the cap tube requirement change if you change the compressor type?

    The cap tube size and length is based on the refrigerant flow required for a specific evaporating and condensing temperature, if the refrigerant and cooling capacity does not change.

    If all else remains constant, except for the compressor type you should be OK to replace the compressors. The compressor type (piston or rotary) should have no effect on the cap tube.
    If all else fails, ask for help.