08-05-2007, 03:10 AM #1
mcquay centrifugal chiller 063 compressor
we were having a oil loss problem we went through the mcquay oil loss trouble shooting guide , the last thing we checked was the inlet guide vane o rings they checked ok the only two things left are the low speed shaft seal and the high speed shaft seal , but we do not have any of the special tools if required to proceed further are there any needed to check and or replace these seals and does anyone have a better proceedure on how to check these two seals for the oil loss problem
09-05-2007, 03:51 AM #2
Re: mcquay centrifugal chiller 063 compressor
Did you check the oil cooler? How about the mist eliminaters in the oil pump assembly?
11-05-2007, 03:19 AM #3
yes we checked the oil cooler for leaks
and we opened the oil assembly to find that there are no mist eliminaters in this pump assembly but we did change the seperator seal while the oil pump was apart
22-11-2010, 05:58 PM #4
hi,
We are facimg a problem to remove the cone assembly of the WDC 100 compressor it is not coming out. ist it possible by remove the bolts and can pull out?. the vanes are closed position. is it required to be open or do any thing?.Any one femilure with this pls help us.
Thanks.
22-11-2010, 06:40 PM #5
With the McQuay's and Mitsubishi's an oil pressure alarm does not necessarily mean there is an oil problem.
Of course - if you are actually seeing the oil drop in pressure then it possibly is an oil pressure problem. Otherwise I must ask why do you think it is an oil pressure problem?
Can’t get a brine chiller down to temperature.
By dkemper in forum Trouble ShootingReplies: 8Last Post: 08-06-2007, 03:38 PM -
Mcquay PES Flooded Water Cooled Screw Chiller
By Brian in forum Technical SpeculationsReplies: 4Last Post: 05-07-2006, 09:43 PM -
Chiller coldroom compressor problems.
By Lucas in forum Trouble ShootingReplies: 27Last Post: 24-12-2004, 11:30 AM -
Compressor pumping efficiency
By shogun7 in forum FundamentalsReplies: 0Last Post: 25-02-2004, 10:50 PM -
One Half of a Part Wound Compressor Motor is Burnt
By aygul in forum Trouble ShootingReplies: 2Last Post: 25-08-2003, 11:11 AM