    Unhappy Orifice Plates



    Can anyone give me some information on orifice plates, as a metering device, please?


    Tony

  2. #2
    Join Date
    Mar 2001
    Location
    Derby, England
    Age
    58
    Posts
    86
    Rep Power
    24
    Tony

    What info are you looking for specifically? Let me know and I'll try and help you out.

    Frosty

  3. #3
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25
    Any info really. Its just that I've never come across them.

    What sort of systems would use them?
    Why they would be used, as opposed to other metering devices?
    How do they work- is it just like a capilliary tube?
    Tony

  4. #4
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Tony, oriface plates can be used in replacement for electronic expansion valves on flooded systems. Usually used to meter liquid to evaporators in pairs, each equiped with a solinoide valve. One off pulse/bleed solinoid to keep the flow in the system moving and one on pulse/main to feed the main liquid to the evaporator and in some cases to over-feed the evaporator for liquid subcooling purposes. Switching of the main valve/oriface plate is by High Pressure Float switch, Low Pressure Float Switch or on the degree of liquid subcooling accross a heat exchanger, as in a Low Pressure Receiver System.
    Other aplications for an oriface are oil metering on simple oil return lines from separators or small fixed load refrigeration coils where a means of separating liquid, such as an accumulator has been fitted (oil coolers and refrigerant purgers).
    I hope this is of some help, post again if you require any clarification or just more information.
    Regards. Andy.
    If you can't fix it leave it that no one else will:rolleyes:

  5. #5
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    The short tube orifices, aka, "plug" orifices, used in the majority of residential a/c and heat pump systems are essentially orifice plates. They are a precisely formed hole for refrigerant to flow thru. The flow equation for an orifice is:

    m = C<sub>f</sub> * A * (2 * g<sub>c</sub> * <FONT FACE="Symbol">r</font> * <FONT FACE="Symbol">D</font>p)<sup>1/2</sup>

    where:
    m = refrigerant flow, lb<sub>m</sub>/sec
    C<sub>f</sub> = flow coefficient
    A = area of orifice, ft<sup>2</sup>
    g<sub>c</sub> = gravitational conversion factor, 32.174 lb<sub>m</sub>-ft/lb<sub>f</sub>-sec<sup>2</sup>
    <FONT FACE="Symbol">r</font> = refrigerant density, lb<sub>m</sub>/ft<sup>3</sup>
    <FONT FACE="Symbol">D</font>p = pressure drop across the orifice, lb<sub>f</sub>/ft<sup>2</sup>
    Last edited by Prof Sporlan; 20-07-2002 at 03:27 AM.
    Prof Sporlan

  6. #6
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25
    Thanks Andy and Prof Sporlan.

    Your help and information is much appreciated.
    Tony

Similar Threads

  1. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Replies: 111
    Last Post: 13-04-2010, 08:58 PM
  2. Cold plates
    By Peter_1 in forum Commercial
    Replies: 1
    Last Post: 10-05-2006, 07:52 PM
  3. Eutectic plates
    By Temprite in forum Commercial
    Replies: 12
    Last Post: 31-05-2005, 12:13 PM
  4. superheat with the wrong orifice
    By superheat in forum Air Conditioning
    Replies: 9
    Last Post: 25-10-2002, 08:54 PM
  5. Orifice
    By reggie in forum Fundamentals
    Replies: 13
    Last Post: 11-10-2002, 10:56 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •