    Smile data rooms



    Whats the best method to cool data rooms ?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: data rooms

    Just so that we get the wording right, what do you classify as a 'Data Room', what sort of equipment is within it?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: data rooms

    CCU = Close control units.

  4. #4
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: data rooms

    Some sort of air conditioning... perhaps?

  5. #5
    Join Date
    Aug 2001
    Location
    ireland
    Posts
    34
    Rep Power
    0

    Re: data rooms

    Quote Originally Posted by Brian_UK View Post
    Just so that we get the wording right, what do you classify as a 'Data Room', what sort of equipment is within it?
    servers for telecom (not blade servers) at present served by 3 uniflair dx downflow units which are tempermental. So our customer is looking for alternatives.
    Load approx. 240kW

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: data rooms

    Quote Originally Posted by techni View Post
    servers for telecom (not blade servers) at present served by 3 uniflair dx downflow units which are tempermental. So our customer is looking for alternatives.
    Load approx. 240kW

    www.montair.it

  7. #7
    Join Date
    Aug 2006
    Location
    Canada
    Age
    61
    Posts
    149
    Rep Power
    18

    Re: data rooms

    Downflow units? I assume from this that you are referring to a data room with a raised floor.

    The unit that I have worked with the most frequently is made by Liebert. They make downflow units, and also chillers for cooling mainframes etc.

    For up flow units, there is a variety of units I have seen, Carrier, ComfortAire, Chrysler, not certain if Liebert makes them.

    Liebert is truly the Cadillac of units IMO.

    My question would be...why are the units that you have temperamental?

  8. #8
    Join Date
    Aug 2001
    Location
    ireland
    Posts
    34
    Rep Power
    0

    Re: data rooms

    FALSE ALARMS : EG. LOSS OF AIR FLOW, FIRE AND SMOKE, WATER, HP, LP , ALL FALSE WHEN CHECKED OUT.
    Quote Originally Posted by Sledge View Post
    Downflow units? I assume from this that you are referring to a data room with a raised floor.

    The unit that I have worked with the most frequently is made by Liebert. They make downflow units, and also chillers for cooling mainframes etc.

    For up flow units, there is a variety of units I have seen, Carrier, ComfortAire, Chrysler, not certain if Liebert makes them.

    Liebert is truly the Cadillac of units IMO.

    My question would be...why are the units that you have temperamental?

  9. #9
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: data rooms

    All digital inputs, then. I would check the voltage between common and input. If the transformer is weak, then the low voltage may be interpreted as open input.
    Also the connectors and wire terminals must be checked against proper insertion.
    Power surges may cause EMI on signals cables of DIs, too.

  10. #10
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: data rooms

    Have you considered Airedale? Many models available to suit all applications.

    Regards
    Jase

  11. #11
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: data rooms

    What brand are in there now?

  12. #12
    Join Date
    Jul 2006
    Location
    Copenhagen
    Posts
    39
    Rep Power
    0

    Re: data rooms

    We always use Stulz downflow units, and a propane chiller. It is a professionel product, that would satisfy most engineers. I have also tryed Airblue, Montair, Airdale...you name it. Stulz is the best. It has got plenty of servicing space, and a vlt controlled fan.

  13. #13
    Join Date
    Mar 2007
    Location
    Liverpool
    Age
    57
    Posts
    20
    Rep Power
    0

    Re: data rooms

    Hi Condor, I Don't know anybody over here in the uk that uses propane!
    Airedale "alphacool" or "easycool" downflow DX is a good choice, with or without humidification, good units, good controls!

  14. #14
    Join Date
    Feb 2007
    Location
    north west
    Age
    36
    Posts
    243
    Rep Power
    18

    Re: data rooms

    ihave installed a few airedale but the underfloor blow ones but u can get them to blow in all directions anyway, cools the comms room in no time adam

  15. #15
    Join Date
    May 2007
    Location
    Moscow
    Age
    40
    Posts
    82
    Rep Power
    17

    Re: data rooms

    Hi to everyone! I think that every VRF (maybe,Daikin-VRV) system is the best solution of this problem

  16. #16
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: data rooms

    High airflow

    Blow through coils

    Proper air distribution

  17. #17
    Join Date
    Mar 2007
    Location
    uk
    Age
    51
    Posts
    120
    Rep Power
    18

    Re: data rooms

    Hi if your thinking of upgrading to new then i would suggest Airedale or Eaton Willams kit due to there good spares & technical back up being uk manufacturers.

    But with regards to all the false alarms on the present kit, are all alarms flashing on all units or different ones on each, are the units linked together so one common alarm is registered on all units ??. Not familiar with this kit but maybe the parameters of the alarms are not set correct for what ever reason or maybe a bit of paitence is required looking for bad eletrical connections after all most fault voltage wiring usually starts from one place (transformer assuming this has been checked from earlier post). And then is networked around the unit in a mixture of parralell and series wiring through various protection devices (also assumming this kit is old and has an electronic controller but all the protection devices are electro mechanical).

    Also check under the floor for maybe a restriction of the air distribution, maybe a new cable tray has been installed across the room full of cables nicely blocking flow causing the units to throw up various faults, air flow, Lp ect.

    Dont give up on the old kit yet if your like me and just love scrathing your head on site and having a old mooch around, its not always the units fault there has to be a reason.

  18. #18
    Join Date
    Aug 2006
    Location
    Canada
    Age
    61
    Posts
    149
    Rep Power
    18

    Re: data rooms

    Quote Originally Posted by techni View Post
    FALSE ALARMS : EG. LOSS OF AIR FLOW, FIRE AND SMOKE, WATER, HP, LP , ALL FALSE WHEN CHECKED OUT.
    I am assuming that the fire and smoke alarm is local to the unit, not a separate fire alarm system.

    For all 3 of the units to be generating these false faults;
    -there must be either a common element that is causing these faults to be displayed, or
    -there must be a design/installation flaw within the installation.

    The nature of these faults makes me think that there is a design/installation problem, not a common element. I am assuming these are 3 stand alone units, and am doubting that there is a loose connection in all 3 units.

    A problem with air flow within the raised floor would not cause a HP alarm, nor would it cause a water leak alarm, regardless of what may have changed in the raised floor.

    You havent indicated any problem with the mechanical components. If the units are functioning and cooling, and the pressures/temperatures are all ok, then I would be hesitant about condemning all 3 units.
    I would consider that this is a control issue only.

    I would have a good look at the control circuit, with the attitude that there is a mistake there somewhere.
    -Check the inrush current of all the contactor coils, and compare the totals to the VA of the control transformer. The transformer must be more than big enough to carry all of the coil inrush currents that it will see at any one time. Often the control transformer supplied with a unit is not big enough to power the remote condensor contactor, or remote devices.
    -Check and see if the control board electronics are powered by the control transformer that powers the contactor coils. If this is the case, add in seperate dedicated transformers that are dedicated to powering the control boards electronics only. I would do this first!
    -Check the output voltage from the transformer. I dont know what voltages you deal with in Europe, but we encounter various voltages in Canada, and it is easy to get the wrong voltage control transformer.
    -Check and see if the secondary of the transformer is grounded, and then check the specs and see if it should be, sometimes it is a requirement, and sometimes it is a no-no, depending on the design of the circuit board.
    -If it should be grounded, make certain that the correct side of the transformer is grounded.

    Are the HP and LP sensors electronic, or are they simply control contacts? Is the TX electronic? If no to both...
    Since this is nothing more than a glorified air conditioner, in a fancy box, I would disconnect the high tech controls, run it temporarily off a return air stat placed in front of the filters, with a temporary HP safety. If you can do this in a way that maintains power to the electronics, but doesnt allow them to trip the unit out, you will be able to run the units, and monitor the control faults at the same time.

Similar Threads

  1. do u have any data on comparison of single screw and twin screw?
    By vuputuri in forum Technical Speculations
    Replies: 5
    Last Post: 22-02-2008, 03:52 PM
  2. Replies: 4
    Last Post: 04-01-2005, 04:04 AM
  3. Refrigerator data
    By Cals in forum Technical Speculations
    Replies: 3
    Last Post: 02-12-2002, 02:47 PM
  4. Domestic refrigerator coolant data
    By Paul in forum Fundamentals
    Replies: 2
    Last Post: 13-10-2001, 10:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •