    safety valves



    Any one know of regs stating changing of safety valves due to age
    I have customer who has been recommended to change them
    by the manufacturer.
    Is this in any regs or are they making work for themselves?.



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24
    Hi, to the best of my knowledge relief valves should be changed every 3 Years, this is more a case of good practice that a mandatory requirement, although some insurance companies require it.
    The Insitute oF Refrigeration have guidance notes which cover that sort of thing.
    Regards. Andy.
    If you can't fix it leave it that no one else will:rolleyes:

  3. #3
    Join Date
    Apr 2001
    Location
    South Georgia
    Posts
    8
    Rep Power
    0
    Depending on where you are. In the USA you are bound by your
    OSHA 1910 Process Safety Management. The general rule is change out every 5 years or after a release. It depends on the following 1) local law 2) insurance company 3) Your Process Safety Management Program which you are bound by.

  4. #4
    Join Date
    Apr 2001
    Location
    Southern England
    Age
    66
    Posts
    123
    Rep Power
    24
    In the UK you are bound by the Pressure System Safety Regulations PSSR that cover use and maintenance. If the system is over 25kW then you must have a examination scheme (WSE) and that would include inspection and functional test of any PRV's. It would be good practice to have a WSE for smaller systems. If a manufacturer recommends replacement and provides evidence of the requirement I believe you would loose a court case if you didn't and the Health and Safety people pop in.

    A history of corrosion or premature failure is all the justification you would need. A single operation on a safety critical system should trigger a replacement.

    If you replace a valve watch the Pressure Equipment Directive and En 378 as a differnt specification or catagory may require you to undertake the Essential Safety Requirement ESR assessment.
    Derek

  5. #5
    Join Date
    May 2003
    Location
    Canada
    Posts
    31
    Rep Power
    0
    5 years in Canada as well

  6. #6
    Join Date
    Apr 2002
    Location
    Pennsylvania, USA
    Age
    55
    Posts
    78
    Rep Power
    0
    The pressure vessel inspectors around here only seem to require they be changed if the inspector cannot read the rating on them.

    I've never had one fail inspection due to age...

  7. #7
    Join Date
    Aug 2001
    Location
    NE Lincolnshire, UK
    Posts
    145
    Rep Power
    23
    Current advice and our insurers say three years but our insurance people say that after the next review they expect that the period will be extended to five years.

    Unfortunately, we cannot extend until after this next review which is after the next cycle of valve replacement is due and we have to change all the valve discharge pipework to suit the new PED style valves that are straight through and not right angled like our present ones So we expect a bill for £6k at least

    What was the problem with right angled ones?

    Steve

Similar Threads

  1. Stainless steel valves
    By Tycho in forum NH3
    Replies: 5
    Last Post: 05-11-2008, 02:16 PM
  2. Hinari and how far to open valves
    By stryker in forum Air Conditioning
    Replies: 6
    Last Post: 14-04-2008, 01:47 AM
  3. Glycol water valves
    By eng_ab in forum Industrial
    Replies: 2
    Last Post: 03-06-2005, 09:15 PM
  4. Positon of tx valves
    By Les Stuart in forum Trouble Shooting
    Replies: 5
    Last Post: 16-11-2003, 04:43 PM
  5. Oil Pressure safety scenario
    By herefishy in forum Trouble Shooting
    Replies: 13
    Last Post: 17-05-2003, 12:42 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •