    cap tubing sizing with multiple evaporators



    Hi All,

    I understand there are standard recommendations for cap tub IDs and lengths (and even number of tubes) for different compressor capacities but these seem to infer the use of a single evaporator. What happens when two or three evaporators are used in the same system? Does one use the same lengths as if it is one evaporator or can this cause compressor over-loading. If no, how does one size such cap tubing?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: cap tubing sizing with multiple evaporators

    Hi and welcome to the forum.

    The cap tube is sized for the evaporator with the compressor being sized as the last thing.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2007
    Location
    Nigeria
    Posts
    8
    Rep Power
    0

    Re: cap tubing sizing with multiple evaporators

    Thanks Brian_UK, Any ideas on methods/computations for sizing cap tubing for evaporators as they increase or decrease in size and/or varying evaporating temperature? Approximates or suggestions are most welcome

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: cap tubing sizing with multiple evaporators

    Download once Dancap from Danfoss.
    Why captubes and no TEV?
    A captube performs only the best at one specific condition which can never be met with multiple evaporators.

    As soon you switch off one evaporator, suction pressure will decrease and your cap tube on the remaining evaporator will have not the right length.

    It's not a good idea and it will perform very bad.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: cap tubing sizing with multiple evaporators

    I think Peter is correct. Cap tubes only seem to work well at one condition. If the system goes through repeated high temperature pull downs or if the evaporator circuit lengths are different this will not work.

    Also, all of the evaporators have to be ON at the same time otherwise you change the suction pressure.
    If all else fails, ask for help.


  6. #6
    Join Date
    Mar 2007
    Location
    Netherlands
    Age
    55
    Posts
    15
    Rep Power
    0

    Re: cap tubing sizing with multiple evaporators

    Hello and welkom,

    It is possible to make a cooling system with multiple evaporators with cap-tube. Whe make them a lot with static evaporators and go with a max of 8 evaporators on one machine.Whe make them for cooling tables for dead people and in laboratory low temp.Only the school books say it is not possible but in practice it is.


    jan willem

  7. #7
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: cap tubing sizing with multiple evaporators

    yes but morgues are rather static and thus equilibrium is easy to make. How ever for a more dynamic system I do not not see it performing well at all.

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: cap tubing sizing with multiple evaporators

    Jan Willem,

    I saw it as a multiple evaporator system where one or two can shut down while the others keeps working.
    In this case, I persist in my view that the evaporators will not fed correctly and the setup is certainly not energy friendly.
    It can work but a 4 cilinder engine can also run on 3 pistons

    On the other hand, if all shut down at the same time,
    then I don't see a problem.
    But what if one evparator has a frost build up? I will see once that compressor.

    This is the same as the multiple capillary injection you often see in Italian or Spain counters

    As long as load and ambient stays within some narrow margins, a capillary is a good expansion device.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Feb 2007
    Location
    Nigeria
    Posts
    8
    Rep Power
    0

    Re: cap tubing sizing with multiple evaporators

    Thanks Gentlemen. Actually the evaporators are static, none of the evaporators can or will be switched off and they are same circuit length. My issue is: using 0.070" ID cap tubing for a home built evaporator of length 900 inches ID 1/2", what length of cap tubing would be ideal? Approximations/Suggestions most welcome. And thanks

  10. #10
    Join Date
    Aug 2006
    Location
    Canada
    Age
    61
    Posts
    149
    Rep Power
    18

    Re: cap tubing sizing with multiple evaporators

    I am a cap tube hater. Why would one attempt this? Is cost the primary consideration here?

    I have been heading down the path of solving persistent unsolvable problems in cap tube systems, by selling the customer on the idea that the cap tube is inferior, and the tx is a better approach.

    Are there apllications where the cap tube will perform better?

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: cap tubing sizing with multiple evaporators

    Perform better? Never!
    Perform cheaper? never!
    Initial cost lower? Allways.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    Feb 2007
    Location
    Nigeria
    Posts
    8
    Rep Power
    0

    Re: cap tubing sizing with multiple evaporators

    yes, cost is plus its static evaporators doing the same thing over and over

Similar Threads

  1. Capillary tube sizing
    By Sledge in forum Refrigerants
    Replies: 7
    Last Post: 16-11-2010, 11:44 PM
  2. multiple evaporators
    By billthomas in forum Technical Speculations
    Replies: 27
    Last Post: 06-06-2007, 07:13 PM
  3. Sizing for Australia
    By dogma in forum Fundamentals
    Replies: 5
    Last Post: 17-03-2006, 10:05 AM
  4. Sizing Condenser to Evaporators for different Applications
    By PHENERGY in forum Technical Discussions
    Replies: 16
    Last Post: 01-04-2005, 06:34 PM
  5. Multiple Evaporators
    By rcz in forum Commercial
    Replies: 8
    Last Post: 22-07-2003, 11:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •