Thread: U2 fault

  1. #1
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    U2 fault



    Hello all.

    Had a Daikin FTXS60FVMA fail on a U2 fault late friday evening.(New install).

    Customer not happy.So checked power supply which was OK and tried a new PCB which did not cure the problem.By this stage it was dark and I had had enough so replaced entire out door unit which fixed the problem.

    Have not had a chance to look into it any further, but was wondering if anyone had seen a similar problem.

    Thanks in advance.



  2. #2
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: U2 fault

    yep we had the same problem on one unit and carried out all of the tests required on the mains suppy as you know U2 indicates supply problem.

    In the end we ended up changing the outdoor unit with no further problems.

    Kind regards
    Lrac

  3. #3
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: U2 fault

    Thanks Lrac

  4. #4
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: U2 fault

    Hi
    We had the same problem on many multi 3MXS52B two years ago in France.
    These units use a seperate power module ( not a single outdoor pcb, maybe it's your case with new RXS60F so check ).
    A defective outdoor fan created a short circuit into the Power Module and then U2 was displayed.
    Even we changed the pcb and PM the outdoor fan fired the new spare parts at start up...
    1 month ago i had this problem on a 4MXS80AZ (first R410A series ) for the same reasons ( this unit was installed in 2002 ).
    The trouble shooting guide do not explain this specific case, there's no update of the service manual...
    On the field i try to test the outdoor fan as well as possible or i usually order this part with the power module.
    Hope this helps
    Kind regards
    cool#9

  5. #5
    Join Date
    Feb 2007
    Location
    Bedford
    Posts
    38
    Rep Power
    0

    Maintenance Report Sheets

    Hi Everone I am currently trying to format a maintenance report sheet with tick list for air conditioning and vent plant.Would be interested
    what type of report sheets you use.

    Thanks
    Freecool

  6. #6
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: U2 fault

    I had the same problem on a RXS50. Also condensorfan defect which blew the PM!

    Why they don't make them in a way this doesn't happen I can't understand! Perhaps to generate more sales??

  7. #7
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: U2 fault

    Quote Originally Posted by Sanderh View Post
    I had the same problem on a RXS50. Also condensorfan defect which blew the PM!

    Why they don't make them in a way this doesn't happen I can't understand! Perhaps to generate more sales??
    Sanderh
    You'll surely interesting by the final answer i received from daikin about this problem
    Hope this help
    rgds
    cool#9
    Last edited by cool#9; 09-10-2007 at 05:16 PM.

  8. #8
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: U2 fault

    Thanx! Makes it a bit clearer at least!!

  9. #9
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: U2 fault

    Quote Originally Posted by cool#9 View Post
    Sanderh
    You'll surely interesting by the final answer i received from daikin about this problem
    Hope this help
    rgds
    cool#9
    That's how we were told to check the fan motors.

    Make sure you take the fan blades off first though a seized motor will appear like it's turning properly if you spin it with the blade attached.

    Motor should turn one and a half turns approx if you spin it between thumb and finger.