    Vacing system & JohnsonsControll V46AB Valve?



    I built a system that has a V46AB-1C in it, do I need isolate this during a vac? or can I just proceed and vac the entire system with out pulling its sensing tube out?



  2. #2
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: Vacing system & JohnsonsControll V46AB Valve?

    Every part in a refrigeration system should be able to survive a vacuum.
    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine

  3. #3
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Vacing system & JohnsonsControll V46AB Valve?

    Not quite, when deep vacing you should protect parts with bellows as not to over strain them.

    Any case I remembered what we did be for with the valves. We isolated them and vaced system broke vac with N2 and placed valve sense back on.

  4. #4
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: Vacing system & JohnsonsControll V46AB Valve?

    Actually, the difference between a low vacuum (29"Hg) and a high vacuum (500 microns) is not much in terms of pressure difference.
    If it can survive a low vacuum, it will most likely survive a high vacuum.

    I'm not sure how else can you remove moisture from the part. Pulling a vacuum is what is normally done.
    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine

  5. #5
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Vacing system & JohnsonsControll V46AB Valve?

    Vacing is primarily for removing non condensible.

    Frankly my brain has gone haywire lately here. It is things with gas filled bellows that are most in danger of being damaged by vacuum. thus such things if possible should be isolated or precautions taken. The valve I am using is not gas filled thus I could have left it in, but better safer then sorry. with thermal statics I have been told during deep vac to put the bulb in cold water or water with ice, I guess the reasoning is to keep pressure in the top of the bellows low as possible its self.

    1:24am here so brain is shuting off now. or has all ready hard to tell now days.

  6. #6
    Join Date
    Mar 2007
    Location
    canada
    Age
    43
    Posts
    47
    Rep Power
    0

    Re: Vacing system & JohnsonsControll V46AB Valve?

    The MG pony,
    I would say vacuum away, have done it lots of times, if in doubt ask Johnson Controls. Also here is a thought, would you pull a vacuum on a TEV? (gas charged power element)
    good luck in your project.
    Goodguy

  7. #7
    Join Date
    Aug 2006
    Location
    Canada
    Age
    61
    Posts
    149
    Rep Power
    18

    Re: Vacing system & JohnsonsControll V46AB Valve?

    Quote Originally Posted by The MG Pony View Post
    . It is things with gas filled bellows that are most in danger of being damaged by vacuum. thus such things if possible should be isolated or precautions taken. The valve I am using is not gas filled thus I could have left it in, but better safer then sorry. with thermal statics I have been told during deep vac to put the bulb in cold water or water with ice, I guess the reasoning is to keep pressure in the top of the bellows low as possible its self..
    I have never heard of this as being a problem? Will this crack the bellows? Are they designed to only flex in one direction? I thought that the pressure in the bulb would only end up driving the valve onto the seat. I cannot remember ever experiencing a problem with this. I always thought that you could vacuum the whole system.

  8. #8
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Vacing system & JohnsonsControll V46AB Valve?

    I'm not sure if the engineer who was teaching me was just being neurotic or if there is an issue, either way it doesn't hurt, so simple to shove the bulbe on ice and no worries Though I do think Sporlan mentiond some thing about it in their PDFs.

  9. #9
    Join Date
    Aug 2001
    Location
    Leominster, MA
    Age
    71
    Posts
    45
    Rep Power
    0

    Re: Vacing system & JohnsonsControll V46AB Valve?

    Thinking of the pressures they survive a vacuum is only about 1 or 2 PSI in the negative isn't it????
    My wife says I don't listen to her....or something like that....

  10. #10
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Vacing system & JohnsonsControll V46AB Valve?

    Quote Originally Posted by hvac01453 View Post
    Thinking of the pressures they survive a vacuum is only about 1 or 2 PSI in the negative isn't it????
    14.7 LBS = 29.9" if I recall correctly
    Last edited by NH3LVR; 07-05-2007 at 01:06 AM. Reason: Spelling