    Dear all,
    Regarding the liquid overfeed system (ammonia), 3 ammonia liquid pump (2 used 1 standby) can be installed in parallel. Its performance is good. Is that possible to install 4 ammonia liquid pump (3 used 1 standby)? What is the factor that should i consider?
    Thanks a lot
    Aug 2005
    5,302
    Re: Ammonia liquid pump
    If the refrigerant pumps are the centrifugal type I would not recommend running more than 1 pump (never in parallel).
    The reason for this is the pumps fight one another due to discharge pressure changes. One pump will run higher pressure than the other adjacent pump. This causes the pumps to change operation on the pump curves. So, one pump will pump more volume at a lower discharge pressure than the other pump.
    Theory says you can run centrifugal pumps in parallel, but in practice it does not work very well.
    If you need more flow, then use a larger single pump is my advice.
    Multiple pumps in parallel are extremely difficult to commission properly.
    Jul 2006
    74
    865
    26
    I have never tried running NH3 pumps in parallel, but you have me curious. I will check the Cornell Pump website and see what they have online.
    http://www.cornellpump.com/
    I have run identical pumps (H20) in parallel with success. They see the same discharge pressure, the discharge line. I do realize that they are differences between identical pumps, but it has worked for me.
    What will NOT work is to use a VFD and attempt to trim one pump to control the output of multiple pumps. The check valve on the VFD pump does not open until it comes up to discharge pressure. You have almost no control. We defeated that problem by running two pumps off of one VFD.
    Aug 2005
    5,302
    I have seen many installations with pumps in parallel and you can "make them" work. I had a long discussion with Cornell about this last year. The gentleman said basically... everyone tries this with limited degrees of success.
    The biggest problem I can see is where you have NPSH problems and cavitation. If a pump is operating under a low head condition, the pump flow goes up as does the NPSH required.
    I think what ends up making this a somewhat livable situation is the excess refrigerant we pumping and that almost invariably the pumps are over-sized for head and flow.
    It is a similar problem to not having the hand expansion valves closed enough for liquid balancing to the evaporators.
    Jul 2006
    74
    865
    26
    As usual Iceman, you were a step ahead of me.
    Aug 2005
    5,302
    Perhaps
    It helps to have some good people on here to keep you on your toes too.
    Jan 2006
    Norway
    1,036
    4
    31
    You guys are obviously using the wrong pump
    Here's what you should be looking at
    -Cheers-
    Tycho
    Jun 2001
    N.Ireland
    1,630
    Quote Originally Posted by Tycho View Post
    Tyco,
    what pray tell is that beast.
    Parrallel pumps do work, but require each to have it's own drop leg.
    Me I would fit one pump and a standby, but what do I know
    Kind Regards Andy
    Jan 2006
    Norway
    1,036
    4
    31
    Quote Originally Posted by Andy View Post
    Tyco,
    Kind Regards Andy
    It's the Kværner centrifugal pump, been produced for over 40 years with little to non design change, can be fitted with both electric, and hydraulig motors (for use on gas tankers or similar places)
    requires a minimum suction head of 1 meter, runs dry and chews gravel with no problems
    The outlet port can be rotated 360 degrees (every 45 degree).
    Only downside I can think of is that it weighs 90 Kg not including the motor, and is a "female dog" handle if you are alone. carrying the new one down two decks works ok, but by the time you have the old one out and on the deck and the new one in place, you need help to carry the old one up...
    Thrust bearings in the center, roller bearing on top, two mechanical seals. as long as you mind the oil level it'll run till the cows come home.
    we run a "exchange system" with them, if you have a break down, we send you a new one, you return the old one and we charge for a overhaul (think it's $1200, hours and spareparts). all bearings seals and o-rings are changed so it's as close to a new pump as it gets.
    one of the guys who designed it has one running a fountain in his garden
    -Cheers-
    Tycho
    Jan 2007
    Canada
    65
    158
    A while ago I worked on gas carrier. We had common discharge for 6 pumps. They worked fine. Certainly, real capacity of each pump was not equal. Some pumps had capacities 10-20% more than others. We had Kvaerner pumps. So no problem on discharge side. I agree with Andy that suction side should be design properly(separate drop leg for each pump).
    Nebraska
    Quote Originally Posted by jessica View Post
    Dear all,
    Thanks a lot
    I've never used more than 2 w/ 1 standby. Size them right.Why complicate the complicated.Calculate to 4:1 and there should be no problem.
    Jun 2006
    jiansu
    38
    I think the hermitic pump is the best in quality. I have used a lot of hermitic pumps in ammonia system. I have met a problem.
    Feb 2007
    58
    158
    Quote Originally Posted by ntfreezer View Post
    You've been lucky then
    A company i worked for 5 or 6 years ago had a run of bad luck with hermetic's.
    From the debris i found in the pumps i'm guessing that the pipe fitters did not do a good job of cleaning grinding dust out of the pipework before welding.
    Destroyed the liquid seal (anti recirculation) on the inlet end of the impellor, and the same on the mating surface of the inlet casting.
    The pumps were a write off, never managed to get decent pressure/flow from them again.
    Inlet strainers are your pumps friend
    Aug 2005
    5,302
    Quote Originally Posted by Plank!
    I might question this. When the strainers get dirty the pressure drop across them could cause the refrigerant to flash off resulting in pump cavitation.
    Jul 2006
    74
    865
    26
    Quote Originally Posted by Plank! View Post
    I would be afraid to apply an inlet strainer on an NH3 pump. Oil at low temps could cause severe cavitation and be almost impossible to remove.
    Mar 2005
    638
    I have to agree here. Maybe a start up sock for a week or so on a new installation.
    Hansen and Teikoku, both work well if installed properly. Most of the problem pumps I have seen have been problem designs.
    Ken
    Feb 2007
    58
    158
    On reflection the idea of strainers before the pump is a bit daft. Certainly i don't remember seeing any on any of our projects.
    The debris probably got there during a pipe modification to reduce oil logging in the standby pumps (4 pumps 1 - 3 running depending on cooler/blast duty) three of them were destroyed by the abrasives left in the pipework.
    Aug 2005
    5,302
    Dirty systems could be considered to be a enemy to hermetic pumps because of the pumps carbon bearings.
  19. #19
    Mar 2008
    india
    5
    hello dear i am sreenu from india canu u help me we riquied ammoina liquied pump for 60 tr at -25 c temp what type of ammoin pump requed hp also tell me and pump supplayers adders tell me thank u
  20. #20
    May 2008
    at the edge of the Arabian Sea!
    73
    36
    A positive displacement Douglas pumps is the answer. I had also been using Mohno pumps effectively for pumping Ammonia liquid,,,,
    Once I couldnt find a liquid pumps so what I could do was to install a mono-block centrifugal water pump to do the j0b for the time being,,,unfortunately it didnt work for long and soon leaked from the seals !
    for good sealing you should choose a positive dispacement pumps or even a centrifugal pumps with double seat and longer gland box to ensure proper sealing