Results 1 to 31 of 31
  1. #1
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Saturated Discharge Temperature



    We refer to SST and SDT, being the saturated suction and discharge temperatures.

    SST is the temperature of the vapor line at the suction pressure.

    SDT should be the temperature on the vapor line at the discharge pressure.

    But, with refrigerant temperature glide and component pressure drops, I'm not sure of the strict definition.

    Can anyone give some clarify?



  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Saturated Discharge Temperature

    Hi there,

    SST is the evaporating temperature and SDT is the condensing temperature.

    These temperatures are constant for "normal" refrigerants but they are not constant for Zeotropic blends. This causes major uncertainty for calculating the evaporator and the condenser.

    In practice we need SST and SDT to measure superheat and sub cooling. Here we assume that the refrigerant dew point at suction pressure is SST and refrigerant bubble point at condensing pressure as SDT.

    I completely understand your concern and there is nothing we can do about it.

    Cheers
    Last edited by lana; 19-04-2007 at 11:04 AM.
    Even Einstein Asked Questions

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Saturated Discharge Temperature

    Being "saturated" in the boiling process it is equivalent to dew point of a zeotropic blend.
    Being "saturated" in the liquefaction process it is equivalent to bubble point of a zeotropic blend.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Saturated Discharge Temperature

    I normally use SCT for the condensing temperature as discharge temperature is a separate point describing another condition. Likewise, SET is the saturated evaporating temperature.

    You could say: SDT - SCT is the equivalent temperature loss for the discharge piping, which is similar to SET - SST is the equivalent temperature loss for the suction line piping. However, I tend to not like the term SDT as then people seem to forget what the actual discharge temperature is used for.

    Actual discharge temperature - SCT = discharge superheat, which provides a value used for evaluating screw compressor operation or the degree of reasonable compression or oil injection or liquid carryover.

    I think it is important to not only use the saturated temperatures but the actual temperatures as well to help make these distinctions.
    If all else fails, ask for help.


  5. #5
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Re: Saturated Discharge Temperature

    I have actually been mis-using these terms in the past.

    If you plot the cycle on the p-h diagram, I have assumed that the intersection of the evaporator process with the vapor line was the SST and the intersection of the condenser process with the liquid line was the SDT.

    After writing the question and reading your comments, I realize why the definitions of SST and SDT have come about in the first place. Clearly from the refrigerant gauge set.

    The gauge measures the pressure at the compressor suction and discharge. These gauge pressures can be interpreted as temperature. But, as lana points out, the question is complicated by glide.

    So, do we use the vapor curve to get the define the SST and SDT or do we now have to specify DEW and BUBBLE point to be clear in the case of glide?

  6. #6
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Saturated Discharge Temperature

    Hi there,

    If you plot the cycle on the p-h diagram, I have assumed that the intersection of the Evaporator process with the vapor line was the SST and the intersection of the Condenser process with the Liquid Line was the SDT.
    In the two pahse region (P-h) , the temperature is constant. SO the evaporation and condensation precesses are happening with constant temperatures.

    I don't understand why you confuse these temperatures ? OR DO YOU ?

    SST = Saturated Suction Temperature = Evaporating Temperature = te
    SCT = Saturated Condensing Temperature = Condensing Temperature = tc

    Now when there is Glide then in the two phase region the temperature is not constant. So the Dew and Bubble definitions come to the game.
    Last edited by lana; 20-04-2007 at 03:23 PM.
    Even Einstein Asked Questions

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Saturated Discharge Temperature

    Quote Originally Posted by lana
    SDT = Saturated Discharge Temperature = Condensing Temperature = tc
    I disagree with this statement. Sorry lana.

    If you take the discharge pressure and convert it to saturation temperature, all you have is the equivalent temperature at the discharge pressure which is not the same as the condensing pressure/temperature relationship.

    A subtle but important point.
    If all else fails, ask for help.


  8. #8
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Saturated Discharge Temperature

    I beg your pardon.
    I corrected the statment. It is not discharge, it is condensing.
    Thank you for that.
    Even Einstein Asked Questions

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Saturated Discharge Temperature

    I hope my statement was not taken as an offense lana. It was only my desire to point out a subtle topic often taken as meaning the same thing.
    If all else fails, ask for help.


  10. #10
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Saturated Discharge Temperature

    NON taken.

    But on second thought I think the statement:

    "Saturated Discharge Temperature" is the same as the " Condensing Temperature". And that is because we say "Saturated".
    On the P-h diagram the actual discharge temperature is point 2 which is after the compressor and its saturated temperature is the same as the condensing temperature.
    Cheers
    Even Einstein Asked Questions

  11. #11
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Saturated Discharge Temperature

    Quote Originally Posted by lana
    On the P-h diagram the actual discharge temperature is point 2 which is after the Compressor and its saturated temperature is the same as the condensing temperature.
    True, since it is on the same isotherm. However, if you include the pressure losses in the piping then all of it changes slightly.

    It is the pressure loss which changes the equivalent temperature losses that can affect component performance.

    I think this is similar to some who use the glide temperatures as a benefit in selecting heat exchangers.

    I believe NoNickName was on the right track when he said we should be using the dew and bubble points. Regardless of the refrigerant type the use of these terms should help to keep the focus on the proper criteria.
    If all else fails, ask for help.


  12. #12
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Saturated Discharge Temperature

    It is good to be corrected by a friend than be embarrassed in the field.

    Thanks a lot.
    Even Einstein Asked Questions

  13. #13
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Saturated Discharge Temperature

    Quote Originally Posted by lana View Post
    It is good to be corrected by a friend than be embarrassed in the field.

    Thanks a lot.
    Now that is sig worthy!

  14. #14
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Re: Saturated Discharge Temperature

    I suspect that the terms SST and SDT will fall out of use because they are not clear when there is glide.

    I agree, "Bubble" and "Dew" Point can not be confused.

  15. #15
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Saturated Discharge Temperature

    Quote Originally Posted by lana View Post
    NON taken.

    But on second thought I think the statement:

    "Saturated Discharge Temperature" is the same as the " Condensing Temperature". And that is because we say "Saturated".
    On the P-h diagram the actual discharge temperature is point 2 which is after the compressor and its saturated temperature is the same as the condensing temperature.
    Cheers
    I use SDT as the equivalent temp/pressure at the compressor flange as most manufacturers rate the compressors as flange to flange. I use SCT as the condensing temp.

    So in stating a rating you could say:
    SST= 25 dF
    SET= 27 dF
    SDT = 112 dF
    SCT = 110 dF
    With this you are allowing the equivalnet of 2 dF line line loss in the suction and the discharge.

    Ken

  16. #16
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Saturated Discharge Temperature

    Quote Originally Posted by TXiceman
    So in stating a rating you could say:
    SST= 25 dF
    SET= 27 dF
    SDT = 112 dF
    SCT = 110 dF
    With this you are allowing the equivalent of 2 dF line line loss in the suction and the discharge.
    That's exactly the same way I try to state these. The only ambiguity that remains is the actual liquid feed temperature, which could be stated as:

    SCT - subcooling = Liquid feed temperature

    And,

    We also have the superheat for either evaporator, suction , or discharge.

    I think it's important to delineate the exact point in the system with the correct terminology so I'm in complete agreement with Ken.
    If all else fails, ask for help.


  17. #17
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Re: Saturated Discharge Temperature

    Quote Originally Posted by TXiceman View Post
    I use SDT as the equivalent temp/pressure
    But that's exactly the problem. At the compressor discharge, you measure a pressure. If you look at the p-h diagam at that pressure, there are 2 temperatures at that pressure bubble and dew.

    So you can't just quote SDT because both bubble and dew are saturated at the same pressure.

  18. #18
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Saturated Discharge Temperature

    The SDT should be slightly higher in temperature because the discharge pressure should be slightly higher than the condensing pressure and the resultant SCT.

    Therefore the SCT might be 35C for ammonia while the SDT should be around 36C or slightly higher. At the same time the actual discharge temperature might be close to say 110C (for a recip. compressor).

    The problem with using only temperatures is that we need a way to describe their relative location on P-H diagram.

    It's almost like we are dealing with glide temperatures, except they are only for the resulting temperature loss due to pressure loss. How's that for muddying up the waters?
    If all else fails, ask for help.


  19. #19
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Re: Saturated Discharge Temperature

    Quote Originally Posted by US Iceman View Post
    The SDT should be slightly higher in temperature because the discharge pressure should be slightly higher than the condensing pressure and the resultant SCT.
    Pressure drop is a different problem since pressure is a point function.

    If you measure the pressure at the compressor discharge, it has a value that we relate to saturated conditions (irrespective of the line pressure drop). Just draw a horizontal line on the p-h diagram. It cuts the saturation at 2 points. When there is glide, these two points will have different temperatures.

    Strictly in terms of definition, this means that we can't just say the SDT is x because you would not know if it was referring to the bubble of dew point.

    This is why I think that SDT is a poor term.
    SBP = Saturated Bubble Point
    SDP = Saturated Dew Point
    would be more appropriate.

  20. #20
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Re: Saturated Discharge Temperature

    We seem to have problems coming to agreement on some of the basic terms.



    http://tinypic.com/view.php?pic=4hl78k5

    The image above shows that the line pressure drops are not part of the discharge pressure reading.


  21. #21
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Saturated Discharge Temperature

    I tried to open your link, but for some reason it would not open.

    I think what we are seeing is getting tangled up in knots over semantics.

    The problem by definition will not produce pure horizontal lines through the 2-phase region. They are tilted.

    The discharge pressure at the compressor discharge service valve must be higher than the condensing pressure. Otherwise, we are discussing a pure theoretical process with no pressure losses. The only way this would really occur is fictitious.

    If we do not include line losses the system is not operating, i.e., no flow, no capacity.

    In practice, the discharge pressure is higher than the condensing pressure, just as the evaporating pressure will be greater than the suction pressure (at the compressor). If we are trying to convey this operation with saturated temperatures as the descriptive values this is what we would see.

    SDT > SCT
    SET > SST

    This simple fact when plotted on a P-H diagram would imply the actual plots do not follow the isotherms. In fact, they would look like "an equivalent glide temperature" as a deviation from a theoretical cycle.
    If all else fails, ask for help.


  22. #22
    Join Date
    Feb 2007
    Location
    UK
    Age
    55
    Posts
    53
    Rep Power
    18

    Re: Saturated Discharge Temperature

    Dew point refers to the refrigerant in a gaseous state and since we require superheat at the compressor inlet when measuring the pressure at the compressor we should refer to dew temperature,the same applies to discharge gas leaving the compressor as this is superheated also.
    I agree the confusion comes when in the saturated state however for both evaporators and condensers we can measure the pressure and then take a mean temperature of both dew and bubble points known as mean pressure.You will find most heat exchanger manufacturers refer to mean pressure and you can get some compressor manufacturers that refer to mid-point temperature,copeland select 6 comes to mind as this software enable you to size an evaporator based on expected line losses.
    Hope this helps even if only a little.

  23. #23
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Re: Saturated Discharge Temperature

    Quote Originally Posted by wkd View Post
    ...refer to mid-point temperature, copeland select 6 comes to mind as this software enable you to size an evaporator based on expected line losses...
    Hi wkd, That's all we need now. Another definition of temperature.


    USIceman, As I posted that comment, I knew you were going to refer to pressure drops.

    But, you are not getting my point.

    When you measure the pressure at the compressor discharge port, you are reading a single value.

    The horizontal line on the P-h diagram is just to read the scale. It also indicates that at that pressure there are 2 temperatures (bubble- and dew-) that we use as indicators only.

    Pressure drop doesn't come into the picture yet. We really need to get agreement on a single definition first before we get into the complications of pressure drop.

  24. #24
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Saturated Discharge Temperature

    For me, the word "saturated" is meaningful and distinguishes the use of bubble and dew depending on what phase-change is in process.
    For a liquefaction (condensation), saturated is bubble. For boiling (evaporation), saturated is dew.

  25. #25
    Join Date
    Apr 2005
    Location
    Canada
    Age
    69
    Posts
    23
    Rep Power
    0

    Re: Saturated Discharge Temperature

    According to Dupont at the site http://www.refrigerants.dupont.com/S...pdf/h45938.pdf
    Saturated vapour is the dew point at the outlet of the evaporator. This would assume no superheating in the exchanger.
    Saturated liquid is the bubble point at the outlet of the condenser. This would assume no subcooling in the exchanger.
    The saturation point occurs when the refrigerant is changing state, boiling or condensing. This can also be called the co-incident pressure/temperature point. That's easy for R22 as there is no glide. So the condenser/evaporator pressure can be directly converted to temperature, as they do not change during the condensing or evaporating process.
    With the 400 series refrigerants we still use SST and SDT because they are convenient.
    Be careful when you use the handy charts. Dew point is now the SST and is measured at the outlet of the evaporator. Bubble point is the SDT and is only measured at the outlet of the condenser.
    We often get people reading the pressure at the condenser inlet and converting that to temperature using the charts.
    Better still throw away the charts and use the electronic temperature probes. They are cheap and reliable.

    Binman54

  26. #26
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Saturated Discharge Temperature

    I think we are overly com=licating this whole issue. The A/C folks and the refigeration folks speak a slightly different language when it comes to ratings. One thing to do here is get away from 400 series and the glide issues for this discussion. (I hate 400 series).

    Lets look at a R717 compressor rating.

    The namufacturer rates the compressor bare flange to bare flange so SDT is the ame as SCT as far as they are concerned. Rate your compressor for 100 dF condensing temperature and you know the compressor is rated at 211.9 psia and no discharge losses. To allow for discharge losses, rate the compressor for 101 dF SDT. This is th epressure equivalant to saturation at 101 dF or 215.2 psia which allows for 3.3 psi line loss to the cendenser which is operating at 10 dF CT or SCT.

    With the SDT of 101 dF we do not know where the actual discharge temperature lies.

    To do a preliminary design on a compressor I'd select it for 101 SDT and say 30 SST, but the system would design for 100 dF SCT and 32 dF SET. This allows for the equivalent of 1 dF discharge line loss (3.3 psi) and 2 dF equivalant suction line loss (2.55 psi). This also does not indicate any superheat in the suction.

    Anyway, that is my nickles worth.

    ken

  27. #27
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Saturated Discharge Temperature

    Quote Originally Posted by NH3simman
    The horizontal line on the P-h diagram is just to read the scale. It also indicates that at that pressure there are 2 temperatures (bubble- and dew-) that we use as indicators only.
    If we consider the refrigerant as one not having a glide, there will be only one temperature on each isotherm. In other words, the dew point and bubble point are the same for each isotherm.

    If the refrigerant has a glide, the deviation from a saturation temperature (re isotherm) is the offset due to the glide and would require reference to either the dew point or the bubble point. I think this is the way it is shown in the RefProp program. Anyway, that's my understanding.

    TXiceman brings up some good points also. So far we have been discussing the nature of the refrigerants whether in a operating system or a theoretical cycle.

    The real problem is being able to arrive at a common language to ensure proper application of components. This can be a whole new thread unto itself as there are differences between commercial refrigeration and industrial refrigeration or HVAC.
    If all else fails, ask for help.


  28. #28
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Saturated Discharge Temperature

    I vote for using "SCT" saturated condensing temperature, and against using "SDT". I don't think "discharge" adds anything but confusion. I also prefer "saturated evaporation temperature to saturated suction temperature. Regardless, the dew point and bubble point thing has always confused me. I think of "dew point" as when liquid condenses, and "bubble point" as when liquid boils. So why do we use dew point to judge the evaporation process and bubblepoint to judge the condensing process?

  29. #29
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Saturated Discharge Temperature

    Quote Originally Posted by Dan
    So why do we use dew point to judge the evaporation process and bubble point to judge the condensing process?
    I have always referred to the definitions as you stated them Dan. But, the above comment kind of throws me.

    The dew point curve is on the right side of the p-h diagram while the bubble point is on the left side. Everything to the right of the dew point curve is superheated, while everything to the left of the bubble point curve is sub-cooled liquid. And, everything between the two lines is a two-phase mixture of varying degrees of liquid and vapor.

    I can't say I have ever heard of the the description you provided in the quote above. Has anyone else heard this before?
    If all else fails, ask for help.


  30. #30
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Saturated Discharge Temperature

    I can't say I have ever heard of the the description you provided in the quote above. Has anyone else heard this before?
    I just think it odd.. almost backwards, and there is probably a reason that escapes me... to describe the important temperature/pressure measurement of the evaporation process as "Dew point" and the important temperature/pressure measurement of condensing as "Bubble point."

    I have no problem remembering which is important. I just remember that they are intuitively backwards. But I bet there is a good reason out there that I am missing.

  31. #31
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Saturated Discharge Temperature

    Here is some interesting info... This is a little bit of high brow reading material but it might be useful to some.

    http://lorien.ncl.ac.uk/ming/distil/distilpri.htm

    http://en.wikipedia.org/wiki/Vapor-liquid_equilibrium

    http://www.wlv.com/products/databook...ta/db3ch15.pdf

    This one has some decent information also (see page 10 for a description of bubble and dew points)
    http://www.icorinternational.com/lit...e/PDF/tmes.pdf
    If all else fails, ask for help.


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •