    Re: Estimating refrigerant charge

    It's already been done.

    Look at the excel calculator on the DEFRA site. It is intended to estimate the contained charge within a system in accordance with the EU regulations on Fluorinated Gases.

    http://www.defra.gov.uk/environment/...fgas/index.htm

    Containment assumptions have already been refined for the component parts of a system.



    .

  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Estimating refrigerant charge

    Thanks a lot Argus.
    Appreciate that.
    Even Einstein Asked Questions

  3. #3
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Estimating refrigerant charge

    Dear Argus,
    I tried the programme but it doesn't take into account the volume of evaporator and the condenser?
    Also the suction and discharge line volumes.

    Any comments?
    Cheers
    Even Einstein Asked Questions

  4. #4
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Estimating refrigerant charge

    Yes, I think it does. Please read the data list in the Introduction tab.

    The author has given a choice of common types of heat exchangers and piping arrangements and made assumptions on the partial phase containment in each case.

    It is not a definitive tool, but one designed to give a close indication of the containment of most common system types.

    The calculator was developed for the UK F Gas Stakeholders’ group who are advising on the EU Fluorinated gas regulation. This Regulation demands regular leakage inspection of all systems containing F Gases, above 3 kg, so a containment calculator is essential.

    I won’t place the author’s details on the open web without his permission, but you can contact him through DEFRA or Enviros.

  5. #5
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Estimating refrigerant charge

    Thanks Argus I will check.
    Cheers
    Even Einstein Asked Questions

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •