    Fresh air requirement question



    Hello I have a customer who has asked for a high wall mount inverter h/p & for a separate fresh air supply! it is for an office within a factory environment, office size = 40 cubic mts, max bodies = 10.... they don't want anything too sophisticated.. was thinking of a 4" duct fan with fresh air intake grille run from it's own separate electrical supply switch ( they can then operate it at will) The room is approx 4 to 6mts from exterior. I realise the a/c will have to be sized accordingly to cope with added fresh air gain ! would 8 litres per second per person be near ? at present our design source is unavailable.. can anyone give me some ideas/calcs etc.......thanks



  2. #2
    Join Date
    Nov 2006
    Location
    Australia
    Age
    59
    Posts
    14
    Rep Power
    0

    Re: Fresh air requirement question

    Hi stevo
    Check out ASHRAE or similar governing bodies for the required air change for an occupied office airconditioning application. General cooling load W/m2 (air conditioned area) for a general office can be as high as 180 W/m2. Take into account the heat load from lighting, computers, fax machines etc. 8 litres per second per person is a bit extreme for fresh air make up...... are they on fire??? I would'nt have a manual switch for the office staff to operate at will. Put it on a timer to suit occupancy hours with manual overide or cycle it with operation of the aircon system, whatever you do, just cover yourself by not doing it on the cheap just to satisfy the client, if it doesnt work your phone will be ringing....

  3. #3
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Fresh air requirement question

    Last edited by Temprite; 15-04-2007 at 12:44 PM.

  4. #4
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Fresh air requirement question

    is there not a place on the indoor unit that u can fit a fresh air duct onto?

  5. #5
    Join Date
    Feb 2006
    Location
    England
    Posts
    64
    Rep Power
    19

    Re: Fresh air requirement question

    Quote Originally Posted by thebigcheese View Post
    is there not a place on the indoor unit that u can fit a fresh air duct onto?
    No not on the high wall mount systems !....cheers

  6. #6
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Re: Fresh air requirement question

    Quote Originally Posted by stevo View Post
    would 8 litres per second per person be near ?
    8 l/s/p is a bit high.

    If there is no smoking, you can go down to 2.5 l/s/p for a typical office. Fresh air is a big load so you should keep it to a minimum.

    You are right to base the quantity on the number of people. I have seen estimates based on a fraction of the supply air but this is when you don't have any better figures.

  7. #7
    Join Date
    Feb 2006
    Location
    England
    Posts
    64
    Rep Power
    19

    Re: Fresh air requirement question

    Thanks for your replies ! anyone else with ideas ?

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Fresh air requirement question

    CIBSE guide recommends 8 l/s/person as a minimum fresh air requirement (20 l/s/person for airconditioned spaces) or 6 air changes per hour for an office environment.

    So, for 10 persons you would require 80 l/s or 0.08m3/s or for 6ACH you would require 0.67m3/s.

    The additional cooling load, UK conditions would be 1.51kw or 1.26kw respectively

    0.08m3/s would require a duct @ 150mm dia to give a reasonable velocity and pressure drop.
    Last edited by frank; 16-04-2007 at 07:52 PM.

  9. #9
    Join Date
    Feb 2006
    Location
    England
    Posts
    64
    Rep Power
    19

    Re: Fresh air requirement question

    Many thanks Frank, Just the info i can use !

  10. #10
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Re: Fresh air requirement question

    Quote Originally Posted by frank View Post
    CIBSE guide recommends 8 l/s/person as a minimum fresh air requirement (20 l/s/person for airconditioned spaces) or 6 air changes per hour for an office environment.
    Good advice, always check your local requirements.

    In SA with +35degC ambient and poorly sealed buildings, we try to keep the fresh air to a minimum.

    ASHRAE does not actually give a fresh air recommendation but rather a guideline.

  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Fresh air requirement question

    Quote Originally Posted by nh3simman View Post
    ASHRAE does not actually give a fresh air recommendation but rather a guideline.
    The English CIBSE Guide is also a "Guide" but it is adopted by most design engineers to be incorporated into new build projects, as it sets a baseline for the performance of the services.

  12. #12
    Join Date
    Sep 2005
    Location
    South West
    Age
    50
    Posts
    129
    Rep Power
    19

    Re: Fresh air requirement question

    Quote Originally Posted by stevo View Post
    Hello I have a customer who has asked for a high wall mount inverter h/p & for a separate fresh air supply! it is for an office within a factory environment, office size = 40 cubic mts, max bodies = 10.... they don't want anything too sophisticated.. was thinking of a 4" duct fan with fresh air intake grille run from it's own separate electrical supply switch ( they can then operate it at will) The room is approx 4 to 6mts from exterior. I realise the a/c will have to be sized accordingly to cope with added fresh air gain ! would 8 litres per second per person be near ? at present our design source is unavailable.. can anyone give me some ideas/calcs etc.......thanks
    Both Hitachi & Daikin make fresh air wall mounted splits although i believe Hitachi are dis continuing theirs.

  13. #13
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Fresh air requirement question

    Quote Originally Posted by nh3simman View Post
    8 l/s/p is a bit high.

    If there is no smoking, you can go down to 2.5 l/s/p for a typical office. Fresh air is a big load so you should keep it to a minimum.

    You are right to base the quantity on the number of people. I have seen estimates based on a fraction of the supply air but this is when you don't have any better figures.
    2.5 l/s is bare bones minimum in many places. Think the first number ever used was 4 CFM per in the Houses of Parliament. Heard an urban legend they used to give coal miners 5 cfm per to keep productivity up.

  14. #14
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Re: Fresh air requirement question

    Quote Originally Posted by Abby Normal View Post
    2.5 l/s is bare bones minimum in many places. Think the first number ever used was 4 CFM per in the Houses of Parliament. Heard an urban legend they used to give coal miners 5 cfm per to keep productivity up.
    I wouldn't say 2.5l/s/p is a bare bones minumum.
    We add outside air for 2 reasons
    1. Supply of O2
    2. removal of CO2
    People need 0.2l/s of O2. This is a fresh air rate of 1 l/s/p.

  15. #15
    Join Date
    Feb 2006
    Location
    England
    Posts
    64
    Rep Power
    19

    Re: Fresh air requirement question

    Quote Originally Posted by nh3simman View Post
    Good advice, always check your local requirements.

    In SA with +35degC ambient and poorly sealed buildings, we try to keep the fresh air to a minimum.

    ASHRAE does not actually give a fresh air recommendation but rather a guideline.
    Pheww thank god for that ay !!!