    Ammonia evaporative condenser surface



    Dear Friends:
    Does some body knows the surface area required per MBH at manufacturer std. conditions for a evaporative condenser.
    Best regards
    Gonzalo ARIAS



  2. #2
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    807
    Rep Power
    20

    Re: Ammonia evaporative condenser surface

    It depends on the manufacturing. It is usually from 2kw/m2 ~4kw/m2 . Only for your ref. You can refer to the specific catalogue for it.

    regards
    LC
    I hear...I forget;I see...I remember;I do...I understand

  3. #3
    Join Date
    Jun 2005
    Location
    Quito
    Age
    65
    Posts
    22
    Rep Power
    0

    Re: Ammonia evaporative condenser surface

    Thanks LC
    I think that Vilter, Baltimore, Evapco have about the same surface area, Do you Know this figures? also Kw/m2 that you stated are evaporator KW or total heat rejection KW?
    Best Regards
    Gonzalo

  4. #4
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    807
    Rep Power
    20

    Re: Ammonia evaporative condenser surface

    The ammonia evaporative condenser total heat rejection:2~3.3KW/M2 usually;we made copper tube evap condenser and the heat reject is at the upper level.
    Hope it can do some help for you. You'll design it or manufacture it?

    regards
    LC
    I hear...I forget;I see...I remember;I do...I understand

  5. #5
    Join Date
    Jun 2005
    Location
    Quito
    Age
    65
    Posts
    22
    Rep Power
    0

    Re: Ammonia evaporative condenser surface

    TK, this will help, we use carbon steel pipe.
    Best Regards
    Gonzalo