    Arrow ventilation for refrigeration room



    im working on designing refrigeration rooms for storage of several types of fruits and vegetables.

    as known, the percentage of oxygen and carbon dioxide and ethylene should be controlled. this can be done by ventilating the refrigeration room by a flow rate of fresh air depending on room size and product quantity.

    please help me with the amount of this flow rate required for long term storage.

    best wishes

    Eng. Nedal Iben Ali



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: ventilation for refrigeration room

    You must do this with feedback of the proper sensors, too risky for your product trying to maintain a preset value or a rule of thumb.
    There are special controllers for this task.
    http://www.vdhproducts.nl/ is one possible supplier we see here many times.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    salil sampson's Avatar
    salil sampson Guest

    Re: ventilation for refrigeration room

    hi can i ask a question related to refrigeration?What should be the pressure on discharge line of R404 gas for blast frezeer freezing to -40*c

  4. #4
    salil sampson's Avatar
    salil sampson Guest

    Re: ventilation for refrigeration room

    i meant the correct discharge pressure so that the system does not suffer at low temp

  5. #5
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: ventilation for refrigeration room

    Quote Originally Posted by salil sampson View Post
    i meant the correct discharge pressure so that the system does not suffer at low temp
    Thats sort of like asking

    How long is a piece of string.

    The discharge pressure is dependant on ambient air temp.
    The pressure could be as low as 8 bar or up as high as 22 bar.

    Pressure in refrigeration is not important it just corrisponds to the actual temp.
    Temp is important.

    taz.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: ventilation for refrigeration room

    Spot on Taz, discharge pressure has nothing to do with the evaporating temperature
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Aug 2006
    Location
    Canada
    Age
    61
    Posts
    149
    Rep Power
    18

    Re: ventilation for refrigeration room

    Quote Originally Posted by taz24 View Post
    Thats sort of like asking

    How long is a piece of string.

    The discharge pressure is dependant on ambient air temp.
    The pressure could be as low as 8 bar or up as high as 22 bar.

    Pressure in refrigeration is not important it just corrisponds to the actual temp.
    Temp is important.

    taz.
    I had always attempted to make things work, based on 95 degree F condensing. That is our design conditions for Toronto. When it is colder than that we artifically raise the head pressure, through the use of head master/head pressure controls.

    I agree that the evap and condensor temps are not related, but the design should be to meet highest ambients that the condensor will see. Then one would add additional controls to maintain the head pressure.

    We do however allow the head pressure to drop in cold weather, but we limit that drop to the point where we maintain the pressure differential between high and low pressure required by the refrigerant, rule of thumb is 100psi.

    When we dont do it this way, the evap ends up being starved in low ambients, and freezing up.

    Have I been approaching this incorrectly? Is there another way?

  8. #8
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: ventilation for refrigeration room

    Basically you are correct.

    We have to maintain the pressure differential for the TEV to operate correctly. This also depends on the selection of the TEV nozzle. If the nozzle is selected for a given pressure drop, then this must be maintained otherwise the capacity of the TEV drops therefore, starved evaporator is the result.
    The opposite is also valid. If the nozzle is selected for low pressure difference, and now there is large pressure differential then TEV gives more capacity. We have this problem with the imported second hand units from Europe where the nozzle is selected for low ambient. Here we have higher ambient in summer which results ....in the other hand air cooled condenser is selected for 15°C TD (for Europe) but here we need 8-10°C TD. So you can see the problem.

    Cheers
    Even Einstein Asked Questions

  9. #9
    Join Date
    Jan 2007
    Location
    australia
    Age
    46
    Posts
    49
    Rep Power
    0

    Re: ventilation for refrigeration room

    dicharge temp has a direct relation to evap temp your statement is totally incorrect! if the head pressure drops the suction pressure drops.. i.e evap temp

  10. #10
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: ventilation for refrigeration room

    Quote Originally Posted by setrad7791 View Post
    dicharge temp has a direct relation to evap temp your statement is totally incorrect! if the head pressure drops the suction pressure drops.. i.e evap temp
    To whose statement are you referring to ?
    Even Einstein Asked Questions

  11. #11
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: ventilation for refrigeration room

    Quote Originally Posted by lana View Post
    To whose statement are you referring to ?
    I think he must of been refering to my statement lana.
    I stated earlier that cond pressure did not affect suction pressure.

    Cheers taz.

  12. #12
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: ventilation for refrigeration room

    Hi everybody,

    I would like to discuss something here.

    Actually suction and discharge pressures are inter connected and effect each other.

    If suction pressure rises say for any fault or condition change then discharge pressure rises too. BUT the amount of increase is not the same as the suction pressure.

    The opposite situation is also valid.
    If any HP fault makes the discharge pressure to rise then suction pressure would rise but not with the same amount as the discharge pressure.

    The increase or decrease of pressures depends on the fault.

    Clear example is the excess refrigerant charge fault. If there is excess refrigerant then both pressures would rise BUT the discharge pressure would rise more than the suction, this is why this fault is categorized as High Pressure Fault.

    The only fault which makes the suction pressure rise but the discharge pressure to drop is the compressor fault. That's why this fault is the easiest to diagnose.


    So I should say that setrad7791 is right. Pressures do effect each other and so would the saturation temperatures.

    Cheers
    Even Einstein Asked Questions

  13. #13
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: ventilation for refrigeration room

    Hi, Nedal Iben Ali

    Welcome to RE forums.

    Quote Originally Posted by Nedal Iben Ali View Post
    im working on designing refrigeration rooms for storage of several types of fruits and vegetables.
    as known, the percentage of oxygen and carbon dioxide and ethylene should be controlled. this can be done by ventilating the refrigeration room by a flow rate of fresh air depending on room size and product quantity.
    please help me with the amount of this flow rate required for long term storage.
    best wishes
    Eng. Nedal Iben Ali
    You can use air ventilation/cooling if outside air temperature is lower than you need/have in your cold room at least after harvesting...

    But for long terms storage of fruits/vegetables I think this suggestion is much better

    Quote Originally Posted by Peter_1
    You must do this with feedback of the proper sensors, too risky for your product trying to maintain a preset value or a rule of thumb. There are special controllers for this task.
    Only rooms with controlled atmosphere (CA) can preserve your goods well.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.