    hi fellas iam new to this website and to this game really iam still training and been doing this for about 3 years now and done an nvq 2 but all it is when ihave been to air con units the suction side in the outdoor unit has frozen up solid and ful of ice upto the compressor now i have heard a number of engineers saying that its low on gas just add some, but others say its not the case but also irecently rechared a system with 3kg of r22 which is the exact charge of the system when i started it up the pressures were fine and all working fine but sometimes i can go to the unit and it be froze up and other times its not with no change in pressure so any help would be gratefull thanks alot guys
    11,024
    Re: air conditioning
    Hi Adam and welcome to the forum.
    The sort of problems that you describe can be due to a number of things but a lot more information is needed before an answer can really be given.
    What make/model of unit
    Suction temperature
    Superheat
    Discharge pressure
    Subcooling
    Expansion device
    State of fan/filters/coils
    One problem that used to occur with some of the older R22 units was that they were designed for the Far East and simply froze up in the UK climate; still worked though
    Oct 2005
    IRAN
    878
    Hi there,
    As Brian said we need more info.
    One thing I clear for you about the frost. Seeing a suction pipe frozen up doesn't mean that liquid is coming back to the compressor. It might be because the suction line is cold, so the moisture in the air is frozen on it.
    You can check the followings :
    Measure superheat. If it is zero or very low then you might have a liquid flood back problem.
    If superheat is normal and still you see the frost then it is from the moisture in the air.
    Measure sub cooling. If it is low so the refrigerant charge is low. If sub cooling is OK then the refrigerant charge is OK.
    Again I repeat what Brian said: measure everything then decide.
    Hope this helps.
    Even Einstein Asked Questions
    Apr 2007
    SOUTHAFRICA
    43
    26
    Thumbs up Re: air conditioning
    hozit friend it sounds like it is over charged with refrigerant if it is a cipillary flow control if it is an expansion valve the super heat will need to be set correctly also check the air flow across the evap
    Feb 2007
    north west
    36
    243
    hi guys thanks alot for the quick replys ihave got a few details for you here it is a daikin r125fj7w1 and its a split with a above ceiling indoor unit fancoil the suction pressure is 4 bar and the discharge 16 bar iwent to this unit today just to have a quick look at it and the frost was just a tiny bit when i rubbed my finger across it it went but then half hour later it was thick again also i have seen this quite often on other makes and models not just his one i just thought it might of been something simple but then again what is simple in this game thanks alot adam
    Feb 2007
    north west
    36
    243
    sorry guys the fans and coils on indoor and outdorr are all very clean no problems here regards adam
    Oct 2005
    IRAN
    878
    Hi Adam,
    I assume it is R22.
    If suction pressure is 4 bar(g) then this means that evaporating temperature is just about 0°C which is low for an air conditioner. This is why the frost is building up. Probably the evaporator coil has some frost on it.
    There is a low pressure fault. Check the followings :
    1- Lack of refrigerant.
    2- Expansion device problem or blockage.
    3- Any blocking in the liquid line, like filter or ...
    3- Evaporator. Fan is working properly, any frost on the evaporator, Air filter , ...
    The first three make the superheat to increase and the last one make the superheat decrease.
    Hope this helps.
    Feb 2007
    north west
    36
    243
    yes r22 ihave spoken to daikin and checked these pressure and they say they are fine so now that has confused me the indoor unit (evaporator) is not freezing up thanks adam
    Oct 2005
    IRAN
    878
    Hi adam,
    I said probably.
    How can 0°C evaporating be OK for an air conditioning ? Think yourself.
    I would like to add something. You said that the thickness of the frost changes. This means that the suction pressure fluctuate. I suggest that you monitor the readings for a longer period to see the changes. This would point out the problem.
    cheers.
    11,024
    Quote Originally Posted by lana View Post
    Actually Lana that is about normal around here, superheat brings it back up 8-10K.
    We tend to dehumidify and the units don't always run that hard.
    Feb 2007
    north west
    36
    243
    thanks lana as you can see ihave only been doing this for just under 3 years and apprieciate all your help but ihave always been tought and shown that 4 bar or just over is perfect all your help is well apprieciated thanks adam also this unit has had 3kg of r22 which is the correct amount of refrigerant for the pipe run etc thanks
    Feb 2007
    north west
    36
    243
    thanks brian was geting worried there for a minute thinking ihave lost my mind especially after not long finishing my nvq level 2 and now on my level 3 thanks alot you guys but still why do alot of units do this ihave seen one unit froze upto ther compressor and on the side of the compressor it looking like a snowman it was that bad thanks again adam
    Oct 2005
    IRAN
    878
    Hi Brian,
    If the superheat was OK and the suction gas temperature was say 8°C then there would be no frost. Only sweaty pipes and compressor suction. If there is a frosted suction or compressor then the suction gas temperature is around or below 0°C. This is the whole idea of superheat.
    Feb 2007
    Australia
    70
    15
    Adam
    What is the room temperature?
    Also the air on and off the coil?
    Is there adequate air flow?
    Feb 2007
    north west
    36
    243
    hi wombat iwill get this info asap thanks but i remember checking the ducting that comes of the fan coil and the dampers to ensure they were open and air flow thanks again will post back asap
    2434rick's Avatar
    2434rick Guest
    Check your superheat and subcooling check filters ect, keep to the basics then work from there hope this helps 2434rick
    Mar 2006
    Malaysia
    48
    233
    Smile Re: air conditioning
    Quote Originally Posted by airconadam View Post
    Hi airconadam
    I suggest that u check the position of the TXV it may be placed wrongly or in a warm position that means the TXV open widely more than required. In turn, the evaporator is overfeeded by the liquid refrigerant causing the flooded back phenomenon in ur system. Othewise, ckeck the TXV it self may it is stuck opened by debris becus u mentioned it is sometimes the ice is formulated and sometimes no....so me think u have movable blockage......thank u
    best regards
    Canada
    61
    149
    Hi Adam,
    I assume it is R22.
    Hope this helps.
    Also check the head pressure. A low head pressure will result in a low back pressure
  19. #19
    analog's Avatar
    analog Guest
    Quote Originally Posted by Sledge View Post
    As will an overcharge of refrigerant. Common rookie mistake. Everyone's looking for that 60 and 225.
    I've seen kids dump 30 pounds into a 6 pound system.
    As these other chaps said, airflow, metering device, etc.