    Removing refrigirant



    I mostly work on the larger chillers and occasionnally have to take out all the refrigirant. The problem is changing the large R-cilinders when they are full and the system not!

    I would like to know if anyone has a simple solution!



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Removing refrigirant

    What sort of problem do you have when changing the cylinders?

    Do you have trouble with venting refrigerant from your connecting hoses ? If so then use hoses with attached valves.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Removing refrigirant

    when removing the refrigirant from the system and one R-cilinder filled up, you have to change to another one.

    The easy way is push/pull, but liquid refrigirant in the
    1/2" hose from condensor to the cilinder will be lost each time the cilinder must be changed. On systems I work on come charged with up to 1200kg. Thus a lot off R-cilinders and too much loss!

    So I'm wondering how you handle this!

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Removing refrigirant

    Admittedly I do not normally use 1/2" hoses but with the smaller sizes I always use a ball valve at the end of the hose so that it can be shut when disconnecting from the cylinder.

    Can you make something similar but with 1/2" valves?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Removing refrigirant

    Quote Originally Posted by Sanderh View Post
    So I'm wondering how you handle this!
    Just put a shut off valve on the end of your hose.

    taz.

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Removing refrigirant

    There are some 1/2 SAE m/fm ball valves (pt n. 93848)in the Yellow Jacket catalogue which i think would screw onto the end of your 1/2 hose.

    Jon

  7. #7
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Removing refrigirant

    I know there are 1/2" valves, but the coupling to the cilinder is the problem!

    I've fabricated something myself, but I was wondering if there's something on the market! I've looked almost everywhere but never found anything suited!

    I'll try and post a picture of the valve i've made.

  8. #8
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Removing refrigirant

    Finally, Bingo!!! Thanks! Never found it before!


    Anyway, here's what i've made!
    Last edited by Lowrider; 22-09-2007 at 10:01 PM.

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Removing refrigirant

    Great, well done and hope it keeps your fingers warmer now.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Removing refrigirant

    Keeps my fingers warm?

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Removing refrigirant

    Quote Originally Posted by Sanderh View Post
    Keeps my fingers warm?
    Sorry,,,, no liquid refrigerant over your hands when disconnecting.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  12. #12
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Removing refrigirant

    Oke! That's right! Never looked at it that way!

    It's just a lot of work changing cilinders and some loss of refrigirant!

  13. #13
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Removing refrigirant

    Can you not make parallel banks of cylinders with a master disconnect manifold

  14. #14
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Removing refrigirant

    i was just going to say the same, if you have twin ports on the cylinders couple two up, in on the vapour tap ,out on the liquid to the vapour tap on the the second cylinder, it helps in other ways too, in summer helps performance and time as your not getting the bottles as hot trying to cram it all in one, try it.

  15. #15
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Removing refrigirant

    Usually what we do is connect the 1/2"hose from the bottom of the condensor to the cilinder. Then from the vapour side draw the vapour with a recovery unit and put it in the evaporator. When the cilinder is full we change it. This way you can get most of the refrigirant out as liquid and safe hours of waiting!

    The tricky part was changing the bottles, since we didn't have a good tool for that!

    Thanks all for oyour thoughts!!

  16. #16
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: Removing refrigirant

    instead of using cyliders and spending days on draining a ton of *****, why don't you contact your local ***** supplier and get a tank, a normal tank holds between 700 and 900 Kg of refrigerant depending on type of refrigerant, they will lend you the tank for a deposit or a low day rate, or you can buy the tank.

    We have two tanks we own, but at any one time the last few years we have had no less than 6 tanks in operation.

    also, we use 10mm Ermeto couplings on all our plants, but finding anything that fits with the flare connections is close to impossible, there are some JEC couplings that go from ermeto to something that fits with 3/8" and 1/4" flare, they are not the same, but the threads match.

    I usually just solder my own connections.

    And I always have a ballvalve close to the bottle connection... just make sure the ballvalve is rated for the pressure, and note that ballvalves designed for refrigeration should have a hole drilled in one side of the ball so as not to trap liquid when it's closed.
    -Cheers-

    Tycho

  17. #17
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Removing refrigirant

    The problem with using a tank is transportation! Most of our machines are in the basement or on the roof. Normally a roof can hold 250kg/m2 and putting 400kg in a tank will go over that! And transporting a tank into a basement is also a lot of work!

    The way we do it, push/pull, we can empty a machine with 1000kg within 6 hours!

  18. #18
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Removing refrigirant

    i,ve got a good bit of kit ,will post a pic of it, my bottle connector is a large hand tighten joby with a gate valve on it, swop bottles with minimal loss, got 1/4 and 1/2", available from polar pumps doncaster,not cheap but worth every penny,

  19. #19
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,036
    Blog Entries
    4
    Rep Power
    31

    Re: Removing refrigirant

    Quote Originally Posted by Sanderh View Post
    The problem with using a tank is transportation! Most of our machines are in the basement or on the roof. Normally a roof can hold 250kg/m2 and putting 400kg in a tank will go over that! And transporting a tank into a basement is also a lot of work!

    The way we do it, push/pull, we can empty a machine with 1000kg within 6 hours!

    Don't look at the problems all the time, look for a solution

    Dynamite my friend... dynamite... works fine no matter if you want to get the tank up or down just need to remember where to place it, depending on what way you want the tank to go
    -Cheers-

    Tycho