    will it work?



    Hi guys. Can i pick your brains i wonder? What i want to know is: can i fit a capillary line if i by pass the receiver to get this unit to work.
    Customer with an upright single door freezer (Gastrnorm type) needed new compressor to be fitted as old one gave up the ghost. Fitted an R404 pot but old one was R12 with non adjusting exspansion device. Teddington i think. Cond unit is up on top of the up-right with a liquid receiver. It runs but only pulls down to 12 degrees C. Freezin up after the valve and sounds like its short when its not.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: will it work?

    Most important readings we need for your problem: condensing pressure, evaporating pressure, SH and SC and used gas.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: will it work?

    OK, give us all a clue... what refrigerant is it running on now?

    Did you need to do an oil change?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    mr fridge man's Avatar
    mr fridge man Guest

    Re: will it work?

    The back pressure is at 20psi running on R404. Not too sure what the head pressure is running at as service valve faulty. No oil change carried out.....

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60

    Re: will it work?

    So, the old system was running on R12 and R12 oil. The compressor has been changed along with the refrigerant but the system wasn't cleaned.

    There is a possibility of the old oil clogging the system as it is not miscible with the R404a.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Mar 2007
    Location
    canada
    Age
    43
    Posts
    47
    Rep Power
    0

    Re: will it work?

    A new 404a compressor should have poe oil in it. Although, you should be certain. If all things are as they should be, you should be able to remove the receiver and install a cap tube.
    But why not just install a 404a tev?

  7. #7
    mr fridge man's Avatar
    mr fridge man Guest

    Re: will it work?

    The long bankholiday easter weekend & the customer needs it working by the monday. Wholesalers are closed until tuesday & i don't have the correct type of tev. If i can by pass the receiver with a cap line and it'll work...... happy days!

  8. #8
    Join Date
    Mar 2007
    Location
    canada
    Age
    43
    Posts
    47
    Rep Power
    0

    Re: will it work?

    5ft of TC 36 (.036inches) capillary line for 404a low temp @ 1/3hp. I know this because I repaired a freezer the other day. I have a chart to figure out different sizes for different tonnage. Let me know if you want a cross. Best of luck.

  9. #9
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: will it work?

    Quote Originally Posted by mr fridge man View Post
    The long bankholiday easter weekend & the customer needs it working by the monday. Wholesalers are closed until tuesday & i don't have the correct type of tev. If i can by pass the receiver with a cap line and it'll work...... happy days!
    Do you have an R 502 valve that would be a good replacement?
    At a push to get it going an R22 valve would work reasonably well.

    taz.

  10. #10
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: will it work?

    Hi Mr fridge-man,

    As Brian said, there is a high possibility that the system is contaminated and changing the TEV to cap tube will not solve anything. The contamination most probably will clog the cap tube.
    The best way in my opinion is to flash the system and get the contaminated oil out - which is not an easy thing to do .
    Best of Luck
    LANA
    Even Einstein Asked Questions

  11. #11
    Join Date
    Apr 2007
    Location
    lancashire england
    Age
    64
    Posts
    36
    Rep Power
    0

    Re: will it work?

    why didnt youput an equivalent comp on and put a replacment gas in like isceon 49l or an equivalent i think you have made a mistake