    Refrigerant Compressor is Sweating



    A certain refrigerant compressed air dryer during operation the refrigerant compressor is sweating**(is always wet) and cause often a short circuit and**the
    protection device (RCD) energised .**Usualy this is caused if a liquid refregerant is returning to the compressor.

    Can you comment please?



  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Thumbs up Re: Refrigerant Compressor is Sweating

    Hi there,
    You have to describe your system more than that. What is the actual application of your system?
    What kind of evaporator is there?
    Is there a TEV or cap tube?
    and many more questions......

    Give us more info.
    Cheers
    Even Einstein Asked Questions

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Refrigerant Compressor is Sweating

    It humid ambients, it is perfectly normal that the suction side of the compressor is sweating. It is not normal that the condensate drips over an electric component and trips it. Just protect the device by making sure any more drop drips over the electric parts.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Refrigerant Compressor is Sweating

    You need to check that the air flow through the drier is as normal.

    Some air drier have a hot gas bypass, or similar, to control the load of the evaporator. You need to monitor the temperatures through the system so that the system operation can be analysed properly.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Jan 2007
    Location
    USA
    Posts
    37
    Rep Power
    0

    Re: Refrigerant Compressor is Sweating

    Could it be that your getting liquid back to the compressor. check your bulb if you have an x-valve and make sure is is all the way down in the well

  6. #6
    bear4rain's Avatar
    bear4rain Guest

    Re: Refrigerant Compressor is Sweating

    HA i work for ingersoll rand as a dryer tech if you tell me the make and model I can probable help you out

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Refrigerant Compressor is Sweating

    Hi B4R and welcome to the forum.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Mar 2007
    Location
    CYPRUS
    Age
    63
    Posts
    21
    Rep Power
    0

    Re: Refrigerant Compressor is Sweating

    Quote Originally Posted by bear4rain View Post
    HA i work for ingersoll rand as a dryer tech if you tell me the make and model I can probable help you out
    .


    I am very happy that we are working in the same field. The dryer is Friulair - Italy- type DFR18 -
    Thanks

  9. #9
    Join Date
    Mar 2007
    Location
    UAE
    Age
    43
    Posts
    78
    Rep Power
    18

    Re: Refrigerant Compressor is Sweating

    Dear all,

    Can you please help me?

    I have to know about the specific heat of MILK KHOA to work out a cold storage calculation.

    Kindly reply to my personal ID :tjk2007@gmail.com

    Thank you Very much.

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Refrigerant Compressor is Sweating

    Quote Originally Posted by tjk2007 View Post
    I have to know about the specific heat of MILK KHOA to work out a cold storage calculation.
    It is off topic in this thread. I don't know what KHOA is, but I assume is milk, like any other cow milk

    Composition of milk:
    87.3 % water
    3.9 % milk fat
    8.8 % solids-not fat
    3.25 % protein ( ¾ casein)
    4.6 % lactose
    0.65 % minerals (Ca, P, citrate, Mg, K, Na, Zn, Cl, Fe, Cu, sulfate, bicarbonate)
    0.18 % acids (citrate, formate, acetate, lactate, oxalate)
    enzymes, gases, vitamins

    Milk Fractions:
    Plasma (skim milk or milk minus fat)
    Serum (plasma minus whey [casein micelles])
    SNF (solids-not fat [proteins, lactose, minerals, acids, enzymes, vitamins])
    Total Milk Solids (fat plus SNF)


    Physical Properties of milkfat: density at 20° C is 915 kg/m3 refractive index (589 nm) is 1.462 which decreases with increasing temperature solubility of water in fat is 0.14 % at 20° C and increases with increasing temperatures thermal conductivity is about 0.17 J/ msK at 20° C specific heat at 40° C is about 2.1 kJ/ kg K electrical conductivity is < 10/ohm cm dielectric constant is about 3.1

  11. #11
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Refrigerant Compressor is Sweating

    Quote Originally Posted by tjk2007 View Post
    I have to know about the specific heat of MILK KHOA to work out a cold storage calculation.
    It is off topic in this thread. I don't know what KHOA is, but I assume is milk, like any other cow milk

    Composition of milk:
    87.3 % water
    3.9 % milk fat
    8.8 % solids-not fat
    3.25 % protein ( ¾ casein)
    4.6 % lactose
    0.65 % minerals (Ca, P, citrate, Mg, K, Na, Zn, Cl, Fe, Cu, sulfate, bicarbonate)
    0.18 % acids (citrate, formate, acetate, lactate, oxalate)
    enzymes, gases, vitamins

    Milk Fractions:
    Plasma (skim milk or milk minus fat)
    Serum (plasma minus whey [casein micelles])
    SNF (solids-not fat [proteins, lactose, minerals, acids, enzymes, vitamins])
    Total Milk Solids (fat plus SNF)


    Physical Properties of milkfat:
    density at 20° C is 915 kg/m3
    refractive index (589 nm) is 1.462 which decreases with increasing temperature
    solubility of water in fat is 0.14 % at 20° C and increases with increasing temperatures
    thermal conductivity is about 0.17 J/ msK at 20° C
    specific heat at 40° C is about 2.1 kJ/ kg K
    electrical conductivity is < 10/ohm cm
    dielectric constant is about 3.1