    Anyone knows ACM Kaelte Klima?
    I attach a photo of the label of one chiller I came across today. It's exhilarating. It's just six months old and the compressor is falling to pieces.
    It's starting every 30 to 60seconds with heavy liquid hits.
    Superheating is nil, and being a R404a, oil is mixed all over the place with refrigerant. The sight glass is full of oil+liquid refrigerant mayonnaise.
    Incredibile piece of horrible engineering.
  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34
    Re: Anyone knows ACM Kaelte Klima?
    http://www.acmonline.it/
    I suppose you found this already NoNickName.
    They seems to be located in the same region as Tasselli, some of their references are in that region.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24
    Look at these three photos: the sight glass filled up with mayonnaise, the oops-I forgot the insulation on the evaporator suction and injection flanges, and the useless inline valve on the gauge capillary (it was much easier to use the schrader connection on the main discharge shut off valve). This last photo specifically shows how even manufacturers ignore the very basic of HVAC engineering.
  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34
    Is the mayonnaise not the oil from the Bock?
    Sorry NoNick but the inline fault doesn't seems a real fault to me.
    The insulation they forgot is indeed very ugly. Isn't this something a service tech has removed and reinstalled badly?
    The cables are also a real mess, all hanging on their cable ties.
  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24
    Quote Originally Posted by Peter_1 View Post
    It's blue and it's a compressor, but not a bock.
    Definitely the oil is from the Frascold iron.
    I don't know, but I don't think so. This unit was installed in late 2006. But I wasn't there for that. So I just had a cigarette looking at it.
  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31
    Hi
    this is almost perfect what you can see in some eastern countries I need a pack of cigarettes looking at some master pieces. Sorry have not some pictures.
    Best regards, Josip
    It's impossible to make anything foolproof because fools are so ingenious...
    Don't ever underestimate the power of stupid people when they are in large groups.
    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts