    Water pipe optimization



    We talk theory about optimization, so let's see how it works in practice.


    In South Africa, we have a power supply problem. A pumped storage scheme was proposed some time ago to pump water to a dam in the Drakensberg mountains. This saves water and produces hydro-electric power during off-peak times. It is apparently a very successful project.


    An ideal (and relatively simple) target for optimization is the stage pipe diameter.


    The total cost of the stage can be simplified to (1) installed pipe and (2) the pumping cost as follows:

    Installed cost of the pipe = 800 x diameter
    Pumping cost = 100x10^12 / (diameter)^
    5

    What diameter would give the least cost?
    Last edited by nh3simman; 03-04-2007 at 07:31 AM. Reason: correct exponents and layout



  2. #2
    Join Date
    Mar 2007
    Location
    India
    Age
    51
    Posts
    39
    Rep Power
    0

    Re: Water pipe optimization

    92.4655 (what ever units). Just did the basic minima calc. Set up a spreadsheet and check the data for yourself.

  3. #3
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    230
    Rep Power
    18

    Re: Water pipe optimization

    Quote Originally Posted by Ravi View Post
    92.4655 (what ever units). Just did the basic minima calc. Set up a spreadsheet and check the data for yourself.
    This answer is not correct.

    Firstly, the minimum can be found by setting the 1st derivative to zero.
    dC/dd = 800 - 100x10^12/d^6 = 0
    gives d = 95.3mm

    But, the answer is wrong for a much more important reason.

    As engineers, we tend to dive in and solve any equation we see without thinking about the significance. Even worse, we use a spreadsheet and fudge a local minima.

    In optimizarion, the problem is much broarder. We need to understand the relationship of this sub-system with the complete system. What I was hoping for was that someone would question the distance between pump stations, the flow rate, the head, and so on.


    Solving a single equation is easy (or maybe not so easy as Ravi has discovered), but finding a system optimization is much more complex.

  4. #4
    Join Date
    Mar 2007
    Location
    India
    Age
    51
    Posts
    39
    Rep Power
    0

    Re: Water pipe optimization

    Curiosity kills the cat and this happens quite often in forums. I mistook the post as a question and not as a quiz. I tought your second equation (for pumping) was based on an existing setup and you deduced it from pump power equation. Never mind it.

    However, the first derivative (or the slope) is 800-5x100x10^12/d^6 and that gives d as 100x(500/800)^(1/6) = 92.4655

    Your answer is based on first derivative of 800-6x100x10^12/d^6, which is wrong.

  5. #5
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    230
    Rep Power
    18

    Re: Water pipe optimization

    Oops, Ravi is right about my slope calculation.

  6. #6
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    230
    Rep Power
    18

    Re: Water pipe optimization

    Hi Ravi,

    In my rush to prove a point, I made a mistake.

    But I think that the point is valid and it doesn't matter that I'm not actually busy with the installation. Sometimes we can play with ideas to find real solutions to problems.

    USIceman has raised the topic of optimization that has got me thinking. what I have tried here is to give an isolated example where optimisation can be done (as you did), but is not necessarily the solution for the system.

    Maybe a better example would be the suction line of a single stage vapor compression cycle. Similar to the above approach, I could optimize the line diameter with no reference to the cycle.

    From basic optimisation theory
    Penalty = Cost of tube + Cost of frictional pressure drop
    subject to some constraints
    1. Velocity for oil return.
    2. Max saturated temperature drop.

    But, would this give me an optimised system. Maybe, I don't know?

    What do you think?

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Water pipe optimization

    Quote Originally Posted by nh3simman
    From basic optimisation theory
    Penalty = Cost of tube + Cost of frictional pressure drop
    subject to some constraints
    1. Velocity for oil return.
    2. Max saturated temperature drop.

    But, would this give me an optimised system. Maybe, I don't know?
    That's an interesting idea. But there are two competing criteria.

    In one you are optimising for the oil return velocity at part load conditions at the sacrifice to full load pressure/temperature loss.

    Conversely, if sized for the full load condition to minimize pressure /temperature loss then the part load oil return velocity suffers.

    Which one should we optimise for? This is one of the predicaments of optimization and overall system design. In some cases, it is a lesser of two evils.
    If all else fails, ask for help.


  8. #8
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    894
    Rep Power
    19

    Re: Water pipe optimization

    Quote Originally Posted by US Iceman View Post

    In one you are optimising for the oil return velocity at part load conditions at the sacrifice to full load pressure/temperature loss.
    Conversely, if sized for the full load condition to minimize pressure /temperature loss then the part load oil return velocity suffers.
    Hi guys,

    In refrigerant pipe sizing, both full load and min. load must be taken into account. For horizontal pipes it is relatively easier, but for vertical pipes .... you have to be carefully for min. load. This is where the double-riser comes into picture, if necessary.
    My point is, if pipe sizing is done according to the standard procedures then it must be optimized, otherwise there will be a huge problem.
    Cheers
    Even Einstein Asked Questions

  9. #9
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    230
    Rep Power
    18

    Re: Water pipe optimization

    Quote Originally Posted by US Iceman View Post
    That's an interesting idea. But there are two competing criteria.
    I don't think that the competing criteria is a problem.

    When you select a tube diameter, you have to satisfy these conditions anyway. If the tube is too big, the velocity will be low and the min velocity criteria kicks in. If the tube is too small, the pressure drop is too high and the pressure drop criteria kicks in. All these two criteria do is give upper and lower limits to the size.

    The ideal tube size could be anywhere between these limits, depending on the first cost + friction loss cost.

    You have to choose some size, so why not the one with minimum cost.

    I think that I'm begining to agree with you about optimizing the sub-system. After all, if this component is at its best then is must contribute to the system accordingly.

  10. #10
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Water pipe optimization

    Quote Originally Posted by nh3simman
    You have to choose some size, so why not the one with minimum cost.
    Unfortunately, that tends to happen more often for that specific reason. It saves money, but I often find these attempts are at odds with overall good system design practices.

    This subject is also sometimes confused with value added engineering. The whole thrust of this always seems to be the desire to make something cheaper under the disguise of cost-effective.

    I am not taking issue with your comment, but only offering an additional viewpoint for consideration.

    I believe what you started off with was similar to economic pipe sizing where you can include the cost of utilities and other crtieria to determine the minimum required pipe size.

    Isn't this fun?
    If all else fails, ask for help.


  11. #11
    Join Date
    Mar 2007
    Location
    India
    Age
    51
    Posts
    39
    Rep Power
    0

    Re: Water pipe optimization

    Quote Originally Posted by US Iceman View Post
    . In some cases, it is a lesser of two evils.
    That is what most of we engineers follow, IMHO. My experience has been in Pharma for 12 years and sometimes I don't feel like justigying my job. Every time you make a conservative estimate, there are distractions interms of bosses and future uncertainities. You will have expansion coming up before you finish a project.

    With pumping and HVAC systems, I heavily bank on variable capacity systems, not for variable loads but to take care of design redundancies. When money is not a criterion, saving your sking should be

    As far as piping is concerned, the biggest drawback in optimization can be commercial availability of different sizes. If we want to optimize then manufacturers may lose. Take bigger sizes, go for VSDs, show some savings and everybody is happy.

    However, I feel the discussions in these technical forums can throw light from many directions and can give us good confidence while trying system optimization.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •