    Angry Heat pump pipe sizing - why bother?



    HELLO!

    For example, on a typical split where the expansion devices are located on the outdoor unit, why is there a difference in pipe size to the indoor? Surely if they are both potentially the suction line then any difference in diameter would impact on the operating pressures?

    And if not then why not have the same size throughout the system?




  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Heat pump pipe sizing - why bother?

    Because the outgoing pipe is part of the "expansion" device.

    If it was a larger diameter then the refrigerating effect would start somewhere along hte pipe and not at the evaporator.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Re: Heat pump pipe sizing - why bother?

    They also operate at different temperatures.
    In heating mode, the outdoor unit is cold.

    -----------------------

    Don't they put expansion devices at both units? (with a non-return bypass)

  4. #4
    Join Date
    Feb 2007
    Location
    podgorica
    Age
    47
    Posts
    7
    Rep Power
    0

    Re: Heat pump pipe sizing - why bother?

    If You draw the refrigerant flow diagram You will see that in both of modes (heat/cool) the tighter pipe is pipe with liquid refrigerant, and other pipe is pipe with gas phase. Density is reason for difference of pipe size.
    If You take other sizes, You will change the capacity and velocity...

  5. #5
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Heat pump pipe sizing - why bother?

    Hi everybody,

    In heat pump system, every calculation - including pipe sizing - are based on cooling mode. Then when switched to heating mode everything is relatively easier
    Cheers
    Even Einstein Asked Questions

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Heat pump pipe sizing - why bother?

    I think Mashan is right: the smallest is carrying liquid with some flash gas in it while the largest one is only carrying pure gas. So density is the answer.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.