    Repair Coplametic 6RA4 discharge valves



    I am having trouble removing head cover plate on Coplametic 6RA compressor in order to replace valve plate. All bolts are loose. Do I just pry at it? (Yes, refrigerant is recovered, no pressure)



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Repair Coplametic 6RA4 discharge valves

    The gaskets are probably holding the valve plate on. You might have to use a small chisel and hammer to tap the valve plate to break the gasket.

    Be careful with this. I seem to remember there being a couple of dowel pins that hold the plate in position on the compressor head.
    If all else fails, ask for help.


  3. #3
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Repair Coplametic 6RA4 discharge valves

    Hello bvis leave two head bolts in the body slightly done up and then use a copper mallet to strike couple of blows in the centre of the head and it should come apart. be careful not damage the suction reed vavle pins.

  4. #4
    Join Date
    Apr 2007
    Location
    North Texas
    Posts
    19
    Rep Power
    0

    Re: Repair Coplametic 6RA4 discharge valves

    If there is an unloader on this head, the two bolts that hold it go all the way through to the compressor body and have to be removed before the rest will come free.

    Yes, I realize the original poster has either completed the repair or scrapped the compressor by now. Just adding this for future readers.
    Last edited by Triggerman; 14-04-2007 at 05:59 PM. Reason: correct spelling

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Repair Coplametic 6RA4 discharge valves

    Hello,

    Welcome from Belgium.

    If you post a question with the units you’re used to work with, place between brackets the other units. So if you normally work with SI units (bar, °C, m³/h..), place then between these units the proper IP units.

    You can do the conversion with a free software program Uconeer
    You can find it on http://www.katmarsoftware.com/uconeer.htm#download
    Or you can use the spreadsheet of Dan posted on http://www.refrigeration-engineer.co...0617#post50617 post 6.

    When you have a technical problem, try to post as many as possible readings you have made. You will see that we need many times condensing and evaporating pressure; discharge, suction, evaporator outlet and condenser outlet temperatures. Try to measure these very accurate.
    The better you measure these, the better we can help you.

    Note also band names, types of all the items installed in the installation.

    I hope that you stay a long time with us and that you can contribute to expand this forum.

    Peter

    PS There's a special section 'New to RE' to introduce yourself
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •