    Hi everyone,
    Does any one have any idea/solution for this problem.

    I had 3 softdrinks bottling lines in one plant. Line 1, line2 & line 3. And each line has a vilter reciprocating compressor which installed totaly separate. What I did is I put them in common, suction & discharge.
    My problem is sometimes I dont get liquid in one of the carbo cooler so the temp of beverage rise up.
    One of the carbo cooler is flooded type the other two is injector type.

    Thanks



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: mojonnier carbo cooler common system

    If the compressors are in a parallel arrangement for suction and discharge, I am assuming the condensers are are connected in a parallel arrangment also.

    How were the receiver(s) re-piped to supply liquid to the carbo coolers?

    It sounds like your liquid is disappearing in the system and not reaching the carbo coolers sufficiently to maintain cooling. That tells me the liquid ammonia is "hanging up" somewhere.

    Is the liquid level disappearing from the receiver(s) when this happens.
    If all else fails, ask for help.


  3. #3
    Join Date
    Mar 2006
    Location
    Philippines
    Age
    53
    Posts
    124
    Rep Power
    19

    Re: mojonnier carbo cooler common system

    Hi US ICEMAN,
    The liquid reciever has no problem there's always ammonia, I'm using only one reciever and condenser's are all in parallel. is there any problem on being different system (lnjector type & flooded type)? Can you give me idea for the sequence of the compressor? load, unload, start & stop of the compressor's for this set up.

    Thanks

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: mojonnier carbo cooler common system

    I can't imagine why the two different feed methods would be operate differently. Both use high-pressure liquid right?

    Which carbo cooler is acting funny? The one that is flooded or the others?

    Is the cooler that is running warm the one farthest away from the receiver?

    Is the liquid level in the receiver constant, or does it fluctuate? I've seen these go from empty to almost full very quickly.

    The systems I have seen are operated off of suction pressure, but the compressors almost always have 100% capacity reduction if the bottling line stops.
    If all else fails, ask for help.


  5. #5
    Join Date
    Oct 2006
    Location
    New Zealand
    Age
    58
    Posts
    29
    Rep Power
    0

    Re: mojonnier carbo cooler common system

    I have had alot of experience with carbo coolers. I service them in New Zealand and overseas. Some of stand alone ones are a critcical charge system ( usually the injector style)and require modifing before they can go onto a common system. A liquid level managerment system has to installed on each one. This require a level switch wired to a liquid level solenoid which will activate whenever the mix pump is going. If you require any detailed info send me a PM and I will see if I can help you further.

    Regards

    Mike W

  6. #6
    halcon's Avatar
    halcon Guest

    Re: mojonnier carbo cooler common system

    Hi, everyone
    Somebody would be able to tell me where can I get the Operation's Manual of the Mojonnier carbo cooler model 10-14?
    Thanks.

  7. #7
    Join Date
    Apr 2008
    Location
    Philippines
    Posts
    12
    Rep Power
    0

    Re: mojonnier carbo cooler common system

    Hi

    It seems, wet and dry suction circuit is in messed up

    mctavara

  8. #8
    m.afiq's Avatar
    m.afiq Guest

    Re: mojonnier carbo cooler common system

    hi

    Does anyone know how to determine the consumption of ammonia for one carbo-cooler. And how many reciprocating compressor is needed to supply 1 carbocooler

    thnks

  9. #9
    Andrew Peller's Avatar
    Andrew Peller Guest

    Re: mojonnier carbo cooler common system

    Hello,

    I am also looking for an operating or maintenance manual for a Mojonnier Carbo Cooler model 14-60.

    thanks

  10. #10
    nick_s's Avatar
    nick_s Guest

    Re: mojonnier carbo cooler common system

    Hello everyone

    I work in a bottling plant with 4 of the lines having mojonnier carbo cooler systems as well as fol mix systems. the problem is that all of the units were purchased used from buying houses as we have no direct contact with the manufacturer.

    Does anyone have any contacts for mojonnier or sccess to their manuals?