    Evaporador drain with poor capacity



    Hello Gents,

    We´re facing problems with a evaporador drain that is not working properly. Almost the whole condensate in the tray is being captured by the airflow (entrainment). Once the evaporador blower is turned off, the drain is able to remove the condensate.

    It is a evaporator configuration where the drain is located in the negative pressure side. I see problems with the 90° bend drain configuration used and the low internal diameter (4 mm). The rate of condensation is 2 liters/hour.

    Does anyone have some material or recommendations for designing the evaporators drains ?

    Thank you,
    Last edited by rhlg; 03-04-2007 at 12:56 PM. Reason: Typing



  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Thumbs up Re: Evaporador drain with poor capacity

    Hi rhlg,

    Drain diam. of 4mm is too small. At least the diam must be 1/2".
    What you can do is to change the drain size first then install a check valve at the end of the drain pipe outside the room. This check valve is the simple and light one. Actually it is a spring operated cap. This will allow the drain water out but it will shut down when the fans are operating. Also we use this cap for preventing any bug getting into the drain.
    Hope this helps.
    Lana
    Even Einstein Asked Questions

  3. #3
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: Evaporador drain with poor capacity

    Install a U-trap at the fan coil unit drain outlet to stop the evaporator sucking air from the drain pipe, water will flow smoothly.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Evaporador drain with poor capacity

    Once you get the drain pipe to a suitable size (remember this is a gravity drain) you should also find out how much negative static pressure you have on the air inlet side.

    The trap height needs to be deep enough to provide sufficient static head so the water does not get sucked back up into the drain pan.
    If all else fails, ask for help.


  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Evaporador drain with poor capacity

    Have a look here for some dimensions and sketches of how it should work....

    Paragraph 6.3.1

    http://www.peci.org/ftguide/ftg/Syst...3_1_Condensate

    This site may be if interest generally...
    Home page - http://www.peci.org/ftguide/index.htm
    Last edited by Brian_UK; 03-04-2007 at 11:00 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Sep 2006
    Location
    Brazil
    Posts
    21
    Rep Power
    0

    Re: Evaporador drain with poor capacity

    Thanks for the feedback. Actually, there is a U-trap at the drain outlet (height of 4 inches of water) to overcome the 3 inches of water negative pressure provided by the blower. The accumulated water is discharged overboard solely when we suck it through the trap (by using mouth).
    Last edited by rhlg; 04-04-2007 at 12:14 AM.

  7. #7
    Join Date
    Mar 2007
    Location
    uk
    Age
    51
    Posts
    120
    Rep Power
    18

    Re: Evaporador drain with poor capacity

    Hi

    Good advice given so take it, increase the drain size, two other things i would check though, is the return air to the unit restricted / not adequate as it will try to suck in where ever it can, also is the fall on the drain adequate it seems from what you describe sucking on the drain outlet causes a syphon effect.