    daikin ac charge problem



    Hi, I'm working on a daikin ducted system with an outdoor unit R125FJ7W1 refrigerant is R22 and the pipe length of about 10mtrs, can anyone help with the correct charge, starting and running current for this unit?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: daikin ac charge problem

    The data you want should be on the plate attached to the unit.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: daikin ac charge problem

    Thread.
    It's my first reply on this forum i hope you'll find answer with the following attachement (pdf).
    cool#9
    Last edited by cool#9; 09-10-2007 at 05:16 PM.

  4. #4
    Join Date
    Jun 2005
    Location
    Hastings, uk
    Age
    72
    Posts
    19
    Rep Power
    0

    Re: daikin ac charge problem

    Quote Originally Posted by cool#9 View Post
    Thread.
    It's my first reply on this forum i hope you'll find answer with the following attachement (pdf).
    cool#9
    Thank you very much for your help on this one, unfortunately the data plate was missing from the unit, thanks again.

  5. #5
    Join Date
    Jun 2005
    Location
    Hastings, uk
    Age
    72
    Posts
    19
    Rep Power
    0

    Re: daikin ac charge problem

    Quote Originally Posted by Brian_UK View Post
    The data you want should be on the plate attached to the unit.
    Thanks Brian but data plate missing from unit

  6. #6
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: daikin ac charge problem

    Colicool
    I checked the data of R125FY1 and the original charge is 3.0 kgs of R22.
    The main difference between R125FJ7W1 and R125FY1 is that the first one is from Daikin Europe Factory so the technical data must be good.
    Regards
    cool#9

  7. #7
    Join Date
    Jun 2005
    Location
    Hastings, uk
    Age
    72
    Posts
    19
    Rep Power
    0

    Re: daikin ac charge problem

    Quote Originally Posted by cool#9 View Post
    Colicool
    I checked the data of R125FY1 and the original charge is 3.0 kgs of R22.
    The main difference between R125FJ7W1 and R125FY1 is that the first one is from Daikin Europe Factory so the technical data must be good.
    Regards
    cool#9
    Thanks again cool#9 hope I can return the favour sometime.

  8. #8
    Join Date
    May 2005
    Location
    manchester
    Age
    49
    Posts
    48
    Rep Power
    0

    Re: daikin ac charge problem

    they are usaully pre charged for a 30 metre pipe run and if a remember its 54grams per metre extra