    capacity control for 100% fresh air dx system



    hi

    I would like to assemble a DX system with 100% fresh air.
    I know that I have to use some capacity control system.
    If I want to use hot gas bypass, which electronic controller I should use,
    and what will be my controlling parameter? (limiting suction pressure, setting leaving air temperature from the coil ...??) and how??

    Best regards

    Coskun



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: capacity control for 100% fresh air dx system

    Suction pressure is the way to go.
    As for the application, I would install a self regulated hot gas bypass, without any electronics. Sporland, Danfoss and other have it in the their catalogue.
    I would prefer chilled water, anyway.

  3. #3
    Join Date
    Mar 2007
    Location
    turkey
    Age
    50
    Posts
    11
    Rep Power
    0

    Re: capacity control for 100% fresh air dx system

    Self regulating hot gas bypass is ok but
    I want high precision controll of set point as well
    If I chose electronic controlle one what shall I do??

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: capacity control for 100% fresh air dx system

    If you want high precision, you need a very fast modulating bypass valve and will cost an arm and a leg. Been there, done that, doesn't satisfy. Electronic control is not a guarantee of good control.
    I would go with chilled water coil.

  5. #5
    Join Date
    Feb 2004
    Location
    USA
    Posts
    132
    Rep Power
    0

    Re: capacity control for 100% fresh air dx system

    Try here: http://www.rawal.com/ these will give you precision control.

  6. #6
    Join Date
    Mar 2007
    Location
    turkey
    Age
    50
    Posts
    11
    Rep Power
    0

    Re: capacity control for 100% fresh air dx system

    I checked the site, it looks like ordinary hot gas bypass valve. what is the benefit or difference?