    Steve Mackie's Avatar
    Steve Mackie Guest
    PHE Secondary Piping
    Looking for opinions and/or common practice:
    On an NH3 to CaCl2/Glycol PHE, which way do you pump the CaCl2/Glycol? Do you PUMP INTO the PHE, or SUCK OUT OF the PHE?
    I would also like to hear reasoning behind which ever way you do it. "It's the way we've always done it" is not a reason.
    Steve
    Aug 2005
    5,302
    Re: PHE Secondary Piping
    My belief is it is better to pump through a device. Almost every system I have seen has the exchangers/chiller/etc. on the pump discharge side.
    There is probably a very good technical reason for doing this, but I'm not sure what it is. Water piping is to me a different field.
    Croatia
    68
    2,261
    Hi, Steve Mackie
    Quote Originally Posted by Steve Mackie View Post
    Steve
    Good question, not easy to explain but
    If we have gravity feed PHE and we have a CaCl2/Glycol expansion tanks divided in two chambers cold/warm it is not good and less easy to install them enough high to obtain gravity feed CaCl2/Glycol to PHE.
    We need some velocity (about o,5-1m/sec) through PHE and for that reason we use primary circuit pumps taking liquid from warm side and pump it through PHE and return to cold side.
    If you install pumps after PHE for sure your pump will run in cavitation area due to low inlet pressure caused by dense liquid and construction of PHE.
    Is this good reason
    But if you like you can try vice versa installation
    Of course maybe I miss something due to lack of information about your system
    Best regards, Josip
    Apr 2006
    Torquay
    59
    130
    There's a lot more to it,but put simply.If you feed a pump through a restriction you will starve it of water causing cavitation.Better to pump through a restriction to stop the pump running off the bottom of its curve.