    PHE Secondary Piping



    Looking for opinions and/or common practice:

    On an NH3 to CaCl2/Glycol PHE, which way do you pump the CaCl2/Glycol? Do you PUMP INTO the PHE, or SUCK OUT OF the PHE?

    I would also like to hear reasoning behind which ever way you do it. "It's the way we've always done it" is not a reason.

    Steve



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: PHE Secondary Piping

    My belief is it is better to pump through a device. Almost every system I have seen has the exchangers/chiller/etc. on the pump discharge side.

    There is probably a very good technical reason for doing this, but I'm not sure what it is. Water piping is to me a different field.
    If all else fails, ask for help.


  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: PHE Secondary Piping

    Hi, Steve Mackie

    Quote Originally Posted by Steve Mackie View Post
    Looking for opinions and/or common practice:

    On an NH3 to CaCl2/Glycol PHE, which way do you pump the CaCl2/Glycol? Do you PUMP INTO the PHE, or SUCK OUT OF the PHE?

    I would also like to hear reasoning behind which ever way you do it. "It's the way we've always done it" is not a reason.

    Steve
    Good question, not easy to explain but

    If we have gravity feed PHE and we have a CaCl2/Glycol expansion tanks divided in two chambers cold/warm it is not good and less easy to install them enough high to obtain gravity feed CaCl2/Glycol to PHE.

    We need some velocity (about o,5-1m/sec) through PHE and for that reason we use primary circuit pumps taking liquid from warm side and pump it through PHE and return to cold side.

    If you install pumps after PHE for sure your pump will run in cavitation area due to low inlet pressure caused by dense liquid and construction of PHE.

    Is this good reason

    But if you like you can try vice versa installation

    Of course maybe I miss something due to lack of information about your system

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  4. #4
    Join Date
    Apr 2006
    Location
    Torquay
    Age
    59
    Posts
    130
    Rep Power
    19

    Re: PHE Secondary Piping

    There's a lot more to it,but put simply.If you feed a pump through a restriction you will starve it of water causing cavitation.Better to pump through a restriction to stop the pump running off the bottom of its curve.