    A local manufacturer wants to quote for transport refrigeration in Dubai.

    With air cooled condenser at 40degC ambient and container temperature at -20degC, thats quite a lift for 1 stage.

    What refrigerant is best for these types of applications?



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Refrigerant for road transport

    Bock FKX50/775N for refrigerated transport, Te=-25°C, Tc=60°C, Tsuction=-15°C, COP=0.80 with R134a

  3. #3
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Re: Refrigerant for road transport

    Quote Originally Posted by NoNickName View Post
    Bock FKX50/775N for refrigerated transport, Te=-25°C, Tc=60°C, Tsuction=-15°C, COP=0.80 with R134a
    Thanks NoNickName, I thought of the Bock and downloaded the FKX catalog from their web site.

    The COP is low, is 2 - stage not an option here?

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Refrigerant for road transport

    Yes it is. Costs are little higher, though.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Refrigerant for road transport

    What about R-507? I was under the impression this was a replacement for R-502, and R-502 systems used to operate in these conditions (or similar to) for many years with conventional equipment designs.
    If all else fails, ask for help.


  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Refrigerant for road transport

    I think R507 would not be compliant to max allowable pressure on high side at that Tc.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Refrigerant for road transport

    Quote Originally Posted by nh3simman View Post
    A local manufacturer wants to quote for transport refrigeration in Dubai.

    With air cooled condenser at 40degC ambient and container temperature at -20degC, thats quite a lift for 1 stage.
    This doesn't strike me as an unusual lift. A bigger condenser perhaps, and a suction/liquid heat exchanger for sure, but nothing here that would warrant a second stage, IMO.

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Refrigerant for road transport

    Quote Originally Posted by NoNickName
    I think R507 would not be compliant to max allowable pressure on high side at that Tc.
    I know. It's higher than R-134a, but this is really not much different than the old days with R-502 and air-cooled condensers.

    R-507 is slightly higher than R-502 (based on memory), but the air-cooled condensers and other equipment should be able to operate under these conditions.
    If all else fails, ask for help.


  9. #9
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Refrigerant for road transport

    I don't know what is the max PS in South Africa. Definitely impossible to use in EU at that Tc.

  10. #10
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Refrigerant for road transport

    How about just buying a Thermo king Magnum
    R404, unit SHOULD !!!! work in ambients up to 50 degrees. i am sure carrier must have an option but just trying to keep reeferjon happy
    http://www.thermoking.com/tk/index.a...euromideafrica

    Regards

    Raymond

  11. #11
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Re: Refrigerant for road transport

    If I look at R507A,



    It is probably a bit close to critical. But, look how the characteristic of the gas squeezes the refrigerating efffect.

    I guess in any event, you are constrained by the compressor manufacturers choice.

  12. #12
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Refrigerant for road transport

    Quote Originally Posted by rdocwra View Post
    How about just buying a Thermo king Magnum
    R404, unit SHOULD !!!! work in ambients up to 50 degrees. i am sure carrier must have an option but just trying to keep reeferjon happy
    www.thermoking.com/tk/index.asp?region=euromideafrica

    Regards

    Raymond

    the fact that thermoking does it, it doesn't mean it either works or it's the best thing to do. I remember Carrier is doing Free Cooling by pumping refrigerant in the condensing coils during winter time

  13. #13
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: Refrigerant for road transport

    the fact that thermoking does it, it doesn't mean it either works or it's the best thing to do. I remember Carrier is doing Free Cooling by pumping refrigerant in the condensing coils during winter time
    Make sure the refrigerant can flow from condenser to evaporator by gravity, then install solenoid valves across compressor and expansion valve. Open the valves and there's your heat pipe...
    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine

  14. #14
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Re: Refrigerant for road transport

    Quote Originally Posted by NoNickName View Post
    I don't know what is the max PS in South Africa. Definitely impossible to use in EU at that Tc.
    What is PS?

  15. #15
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Refrigerant for road transport

    Quote Originally Posted by star882 View Post
    Make sure the refrigerant can flow from condenser to evaporator by gravity, then install solenoid valves across compressor and expansion valve. Open the valves and there's your heat pipe...

    Yeah, sure.
    Aren't we interested in reducing the refrigerant amounts in chillers?
    Isn't refrigerant taxed per Kg in Danmark and Norway?
    What about a refrigerant loss?

    For nh3simman: PS is service pressure, the max pressure allowed by national or international regulations.