    cooling tower's free cooling issue



    Hi Sir
    Who have the real practice for the cooling tower free cooling application? Is it beneficial to retrofit the existed sytem for free cooling? Any concerns

    regards
    LC


    I hear...I forget;I see...I remember;I do...I understand

  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: cooling tower's free cooling issue

    What type of cooling tower? Not all of them are suitable for FC operation.

  3. #3
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: cooling tower's free cooling issue

    Is there any limitation for open or close type cooling tower? The system design may be different but both of them can be used for FC. it's my opinion. Correct me if I'm wrong.

    regards
    LC
    I hear...I forget;I see...I remember;I do...I understand

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: cooling tower's free cooling issue

    No, open type tower cannot be used for FC, and closed type with tap water is a no-go as well.
    Brine must be used. For this, a drycooler is my favourite.

  5. #5
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Thumbs up Re: cooling tower's free cooling issue

    Hi there,

    Cooling process in the cooling tower depends on ambient wet bulb temp. therefore, free cooling is done when the ambient temp (dry and wet) decreases.
    In some applications free cooling can be achieved during winter time.
    For dry cooler the process completely depends on dry bulb temp. Again during winter the fans can be switched off and get some cooling if the application allows. But the pump still runs . so it is not completely free.
    Cheers
    Even Einstein Asked Questions

  6. #6
    MGMS's Avatar
    MGMS Guest

    Re: cooling tower's free cooling issue

    You can do free-cooling with any type of cooling tower, the main factor is air wet bulb temperature. Depending on the type of cooling tower, the system will need to be configured on a different way.

  7. #7
    Join Date
    Sep 2010
    Location
    South Africa
    Posts
    7
    Rep Power
    0

    Re: cooling tower's free cooling issue

    There are some limitations to using cooling towers. Their ability to cool is based on how much water is lost due to evaporation. The evaporation from a cooling tower is based on the quality of air in the surrounding area. If an area has high humidity, less water will evaporate than in a dry climate. In the winter, cooling towers are usually able to cool more efficiently as the air is drier. If the water is needed to be cooled to higher than 75°F, a cooling tower is recommended, dependent upon wet bulb temperature for the region. If water is needed to be cooler, a chiller may be better suited to your cooling needs than a cooling tower.

  8. #8
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: cooling tower's free cooling issue

    20 years ago , airedale produced computer room a-c using free standing a-h-units with the compressor in the same unit , and using glycol for the free cooling by way of a dry cooler< or condencer in sumer<

  9. #9
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: cooling tower's free cooling issue

    It's a very well known setup, and still used nowadays.

  10. #10
    tian.li@189.cn's Avatar
    tian.li@189.cn Guest

    Re: cooling tower's free cooling issue

    yes, it's very popular application of free cooling in HVAC or FC area.
    in winter or cooler season, we can shut down the chiller and use the cooling tower make cool water then supply to working area. this can save huge energy cost of chiller.
    the key problem is the water quality control for the cooling water. so normally recommend close circuit cooling tower which the cooling water will flow inside of circuit to avoid dirty air.

  11. #11
    abdul rasheed's Avatar
    abdul rasheed Guest

    Re: cooling tower's free cooling issue

    Hy;
    i need a ccoling tower For An absorption chiller in pakistan The capacity of Chiller is 3489 KW. Wich cooling tower is best . and what is ideal Range of cooling water For Absorption chiller.

    THanks ,

  12. #12
    chandra159's Avatar
    chandra159 Guest

    Re: cooling tower's free cooling issue

    How to calculate cooling tower capacity & give me basic details

  13. #13
    Daniel Salinas's Avatar
    Daniel Salinas Guest

    Re: cooling tower's free cooling issue

    Quote Originally Posted by abdul rasheed View Post
    Hy;
    i need a ccoling tower For An absorption chiller in pakistan The capacity of Chiller is 3489 KW. Wich cooling tower is best . and what is ideal Range of cooling water For Absorption chiller.

    THanks ,
    HI

    I can help you, could you e-mail me to daniel.salinas@termosolucionessa.com, im from colombia.

    Best regards

    Daniel salinas