    evaporating temperatures



    Hello, I am trying to figure out how refrigerated display cabinets work and their specifcities according to the type of application.

    In the course of my study, I need to identify the typical evaporating temperatures for various refrgieration equipment.

    I was wondering of any of you had an idea of the figures for the evaporating temperatures in a
    *1-door beverage cooler
    *chest ice cream freezer
    *cold vending machine

    It would be of great help.

    I also came up with figures for cooling capacities of the related compressors: do you agree with the following estimates?

    For an evaporating temperature around -10°C
    and a condensing temperature around 40 °C
    *1-door beverage cooler ~0.4-0.6 kW
    *chest ice cream freezer ~ ???
    *cold vending machine ~ 0.5-0.8 kW

    thanx in advance!



  2. #2
    Dave660's Avatar
    Dave660 Guest

    Re: evaporating temperatures

    depends what gas you runnuing on ?

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: evaporating temperatures

    Perhaps you can find the exact data you are looking for from the manufacturers themselves. Most of what you are looking for should be in their technical data for the cases.

    Here are a couple of links to get you started.

    http://www.hussmann.com/

    http://www.tylerrefrigeration.com/
    If all else fails, ask for help.


  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: evaporating temperatures

    Quote Originally Posted by MrsFreeze View Post
    I was wondering of any of you had an idea of the figures for the evaporating temperatures in a
    *1-door beverage cooler
    *chest ice cream freezer
    *cold vending machine

    For an evaporating temperature around -10°C
    and a condensing temperature around 40 °C
    *1-door beverage cooler ~0.4-0.6 kW
    *chest ice cream freezer ~ ???
    *cold vending machine ~ 0.5-0.8 kW
    Wow a US citizen using SI units

    We can say that evaporating temperatures are gas independent.
    You can take as a rule of thumb that the evaporating temperature in commercial refrigeration is 10 K to 15 K lower (smaller evaporators with higher DT) then the desired set temperature.

    As US Iceman said for the power (don't confuse between absorbed and refrigeration power), better look in the catalogs of the manufacturers.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: evaporating temperatures

    Quote Originally Posted by MrsFreeze View Post
    I was wondering of any of you had an idea of the figures for the evaporating temperatures in a
    *1-door beverage cooler
    *chest ice cream freezer
    *cold vending machine

    For an evaporating temperature around -10°C
    and a condensing temperature around 40 °C
    *1-door beverage cooler ~0.4-0.6 kW
    *chest ice cream freezer ~ ???
    *cold vending machine ~ 0.5-0.8 kW
    Wow a US citizen using SI units

    We can say that evaporating temperatures are gas independent.
    You can take as a rule of thumb that the evaporating temperature in commercial refrigeration is 10 K to 15 K lower (smaller evaporators with higher DT) then the desired set temperature.

    As US Iceman said for the power (don't confuse between absorbed and refrigeration power), better look in the catalogs of the manufacturers.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Mar 2007
    Location
    USA
    Age
    48
    Posts
    5
    Rep Power
    0

    Re: evaporating temperatures

    Thanks for your replies!!
    It helped!

    Dave> for appliances running on R134A
    Last edited by MrsFreeze; 20-03-2007 at 09:09 AM.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: evaporating temperatures

    Quote Originally Posted by Peter_1 View Post
    We can say that evaporating temperatures are gas independent.
    Indeed. Similar systems have similar evaporating and condensing temperatures, regardless of the refrigerant used.

    I used to tell people to black out the pressure scales on their guages with a magic marker and directly read the temperature scales for the refrigerant used, because the temperatures are what really matter.

    I quit doing that because with all of the new refrigerants not having scales on the guages, they need P/T charts.

    Still... it's about temperatures, not pressures.
    Last edited by Gary; 20-03-2007 at 05:00 PM.

  8. #8
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: evaporating temperatures

    Quote Originally Posted by Gary View Post
    Still... it's about temperatures, not pressures.
    U betcha SST4ME

  9. #9
    Join Date
    Nov 2003
    Location
    NSW, Australia
    Age
    40
    Posts
    242
    Rep Power
    21

    Re: evaporating temperatures

    Quote Originally Posted by 750 Valve View Post
    U betcha SST4ME
    looks like you have a goof mouth full of that there mate
    "Old fridgies never die, they just run out of gas!"

  10. #10
    mikefitz's Avatar
    mikefitz Guest

    Re: evaporating temperatures

    It's not polite to talk with your mouth full

  11. #11
    Join Date
    Jan 2007
    Location
    australia
    Age
    46
    Posts
    49
    Rep Power
    0

    Re: evaporating temperatures

    1 Single door beverage evap temp -10
    2 chest freezer -20/25
    3 cold vending machine -5

  12. #12
    xpat-Aussie's Avatar
    xpat-Aussie Guest

    Re: evaporating temperatures

    Evap temp should be around 10-15K below set point temp... so a single door beverage unit, would have a set point of around 5(c), therefore, the evap temp should be around -5 to -10(c).
    Chest freezer set point would be around -18(c), giving us an evap temp of around -30(c) et cetera...
    Some freezer applicaitons actually have a suction pressure that is a vacuum... someone already said, "forget about pressure"... best advice I've heard, and the same advice I gave to my apprentices for years!

    So whether you're looking at the high or low side of the system, work in temperature. With so many refrigerant blends around these days, you'll be constantly converting pressure to temperature... but that's why we all have PT charts, they're essential!