    Expansion Valve Selection



    Hi,
    I need the clarification on Expansion valve selection.

    I have the capacity of 87KW
    pressure drop 10 bar
    Refrigerant R22
    Expansion valve Danfoss TEX12 orifice no 4

    This application used a compressor unit of tandem type.Each has the capacity of 41KW.

    Now my question is :
    During the part load application the only one compressor will be running.
    Is this lead any problem to the compressor?

    Basically i need the effect of oversized expansion valve?

    Clarify it.

    Best regards,
    ravi perumal



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,847
    Rep Power
    21

    Re: Expansion Valve Selection

    Quote Originally Posted by raviperumal View Post
    ?

    Basically i need the effect of oversized expansion valve?

    Clarify it.

    Best regards,
    ravi perumal
    The only problem I can see is the pressure difference over the valve.
    The pressure differece must remain about 5 or 6 bar or the valve will fail to work correctly.
    I don't know if that helps but just a thought.

    taz.

  3. #3
    Join Date
    Mar 2007
    Location
    INDIA
    Age
    41
    Posts
    31
    Rep Power
    0

    Re: Expansion Valve Selection

    Hi TAz,
    If valve fails how it will afect the compressor.

  4. #4
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,847
    Rep Power
    21

    Re: Expansion Valve Selection

    Quote Originally Posted by raviperumal View Post
    Hi TAz,
    If valve fails how it will afect the compressor.
    They will fail normaly in one of two ways.

    1 They fail closed, so they reduce the amount of refigerant flow through the system.

    2 They fail open and flood the system with exess refrigerant.

    Both have there own risks attached.

    Cheers taz.

  5. #5
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    894
    Rep Power
    19

    Thumbs up Re: Expansion Valve Selection

    Hi,

    That is the problem and you can not do anything about it. This is why with multiple compressors running in parallel, multiple cycles are used each with its own TEV.
    Except when you use Electronic Expansion Valve.

    Imagine this : The selected valve gives 87kW then when two compressors are running then there is no problem. When one is switched off then there is 43.5kW capacity, i.e. OVERSIZED TEV which will cause a major problem.
    1- high suction pressure, if still there is no flood back to the compressor.
    2- If the evaporator load is reduced more than 50% then you may have flood back to the compressor.

    I have encountered with oversized TEV and it is not nice.

    Hope this helps.
    Cheers.
    Even Einstein Asked Questions

  6. #6
    Join Date
    Mar 2007
    Location
    INDIA
    Age
    41
    Posts
    31
    Rep Power
    0

    Re: Expansion Valve Selection

    Hi,
    When Evaporator load is reduced then the chances of flood back to compressor will be more.

    If i am right,
    In our case the compressor in the upstream line has got failed due to this kind of flood back.

    Yha ....

    Thanks to all.

    Best regards,
    ravi perumal

  7. #7
    Join Date
    May 2006
    Location
    china
    Posts
    98
    Rep Power
    18

    Re: Expansion Valve Selection

    Hi,
    I consider the better design is two EXPs in two branch circuits, and the valves normally should remain 1/3 allowance capacity.

  8. #8
    bamy's Avatar
    bamy Guest

    Re: Expansion Valve Selection

    how can I select an expansion valve for my design of refrigeratin system

  9. #9
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    400
    Rep Power
    18

    Re: Expansion Valve Selection

    If you give the right data to TEX manufacturer, they can advise you better though their software selection program .

  10. #10
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    400
    Rep Power
    18

    Re: Expansion Valve Selection

    You will also need an oil separator in case if you switch off one compressor & operate only one compressor with 50% evap load because your suction line is not designed for part load condition .
    ( on 50% evap load , oil return becomes a problem)
    an oil separator means addition of two nrv in discharge line etc ; your accessories increase to protect the compressor . Hence two independent circuits will be simple to operate & maintain

  11. #11
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    400
    Rep Power
    18

    Re: Expansion Valve Selection

    Hi lana ,
    the system will also need to have condenser capacity regulator to match the fall in evap load

  12. #12
    Join Date
    Jul 2009
    Location
    Brisbane
    Age
    67
    Posts
    79
    Rep Power
    15

    Re: Expansion Valve Selection

    An alternative may be to use an electronic expansion valve. some brands can control down to to well below 40% of total load. The siemens, emerson or sporlan will do the job. Its a matter of preference.

  13. #13
    ijaz ali's Avatar
    ijaz ali Guest

    Re: Expansion Valve Selection