Large refrigeration usually use cooling tower for condensing. What issue should be considered if use evaporative condenser instead of cooling tower? Is the refrigerant side large pressure loss the main factor ?
welcome input!
regards
LC
19-03-2007, 12:43 PM #2
Re: large refrigeration plant cooling tower issue
Dear LC SHI
By using evaporative condensors u can have a better efficiency and decrease power consumption but the main problem with this system is water hardness. Because scales tends to stick to metalic surfaces more than wooden or polymer materials so it affects directly on heat transfer flux.
By the way I have experienced evaporative systems and I prefer this systems to cooling towers or even air cooled condensers in large refrigerations
PirestaniS.P
20-03-2007, 03:43 AM #3
Hi Pirestani
If adding the water softening appliance,how about it to cooling tower?
regards
LCI hear...I forget;I see...I remember;I do...I understand
24-03-2007, 03:05 PM #4
In evap condenser systems, refrigerant is piped directly through condenser sprays.
In cooling tower, you need a condenser water circuit.
Cooling tower can be far from the condenser.
Can be matched to packaged chiller.
No refrigerant piping to do.
Evap condenser needs to be located closer to the compressor.
Gives lower head pressure therefore higher system COP.
Cooling Tower system
Cooling tower
Water pipe network
Condenser pump
Shell and tube condenser
water needs treatment
de-scaling on S&T
Evap cooler system
Evap condenser
Refrigerant piping
water treatment
It would be good to get a response from guys like BAC and Evapco for this question.
25-03-2007, 01:35 PM #5
hi shi.
if u have possibility of water treatment properly, and the distant between ur package and its condenser is not so long, the initial and maintenance costs will be decrease sufficeintly by using evaporating condenser.also the occupied space is smaller than cooling tower or air cooled condenser.
pay enough attention to water leakage.
pirestani.S.P