    fan flow calculation



    please may anybody can help me , how can i calculate the flow of air in CFM if i have the following information
    fan dia = 1000 mm
    fan speed= 1500 RPM
    pich angle= 17(Deg)
    No of Blades= 10
    Motor= 18.5 KW



  2. #2
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: fan flow calculation

    Hello

    The info you gave is a bit sparse
    is it a plate fan , direct drive, what resistance you working against ???

    if it is a centrifugal try contacting NICOTRA fans, as they supply a lot of vent. manufacturers

    If it is a plate/ axial /bifurcated you could try ELTA fans

  3. #3
    Join Date
    Nov 2006
    Location
    Middle East (United Arab Emirates)
    Posts
    43
    Rep Power
    0

    Re: fan flow calculation

    Hi Nasir,
    As you may know, flow rate (in cfm) = Cross sectional area (in sq. ft) * Velocity (ft/minute). You have to find out the velocity. Then only, I think, you can calculate flow rate.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: fan flow calculation

    Or you can contact the fan manufacturer and ask for a fan curve. This curve represents the fan performance at various speeds and static pressure.
    If all else fails, ask for help.


  5. #5
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Re: fan flow calculation

    Quote Originally Posted by nasir View Post
    fan dia = 1000 mm
    fan speed= 1500 RPM
    pich angle= 17(Deg)
    No of Blades= 10
    Motor= 18.5 KW

    If I understand your question, you have certain limited information and need to make an estimate of the airflow.

    There is always a way to make a good guess.

    Motor Power = 1.15 x dp x Q / e

    dp is the total pressure drop, say 500Pa
    e is efficiency, say 65%
    the 1.15 is a number used by some manufacturers to prevent overload.


    18.5 = 1.15 x 0.5 x Q / 0.65
    Q = airflow in cms

  6. #6
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: fan flow calculation

    Very good!
    It bases on the basic physical principle of

    Power = Pressure diff x flow volume

    Make sense
    I hear...I forget;I see...I remember;I do...I understand