    Feb 2007
    36
    10
    non-condensable gas
    hello
    how can you tell that system is running under non-condensable gas and what are the symptoms?
    please can you help?
    mallmk13
    Oct 2005
    IRAN
    47
    893
    12
    Thumbs up Re: non-condensable gas
    Quote Originally Posted by mallmk13 View Post
    hello
    mallmk13
    Hi there,
    If there is non-condensables present OR there is excess refrigerant in the system then you will get the same symptoms. So you have to do a test called "non-condensable test".
    The symptoms are :
    High discharge pressure , High sub-cooling.
    Now I explain the test.
    Pump down the system and make sure that the low pressure setting is low enough to evacuate all the refrigerant from the evaporator. Now when the compressor stops, turn on the condenser fans for at least 30minutes. If there is water cooled condenser then turn on the pump and let the water flow.
    Now measure air (water) inlet temperature into the condenser and record it. With this temperature go to the refrigerant pressure-temp table and find the corresponding pressure in Gauge pressure (not absolute).
    Now compare this pressure with your gauge pressure connected to the system.
    If P(discharge-system) >> P(from table) then you have non-condensables.
    If P(discharge-system) = P(from table) then there is excess refrigerant in the system.
    Remember : this test will not work if the receiver and condenser are in different places with different temperatures.
    I hope this helps
    Even Einstein Asked Questions
    Feb 2007
    36
    10
    ta.. lana
    now it makes sense to me
    Oct 2005
    IRAN
    47
    893
    12
    As US-Iceman said post in one category.
    I have responded to both