    body-iced up(compressor



    hi
    freezer plant runing on 404A high side 200PSI, low side under 1 bar
    evap normal whole body-iced up(compressor).Temp inside cabinet -11 degree
    celcus CAN ANYBODY HELP TO FIND THE PROBLEM?
    THANKS
    mallmk13



  2. #2
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: body-iced up(compressor

    Whats your expansion device? Single or Multi Evaporater?

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Age
    43
    Posts
    9
    Rep Power
    0

    Re: body-iced up(compressor

    single expansion device

  4. #4
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: body-iced up(compressor

    TEV? Capillary?

  5. #5
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: body-iced up(compressor

    Quote Originally Posted by mallmk13 View Post
    hi
    freezer plant runing on 404A high side 200PSI, low side under 1 bar
    evap normal whole body-iced up(compressor).Temp inside cabinet -11 degree
    celcus CAN ANYBODY HELP TO FIND THE PROBLEM?
    THANKS
    mallmk13

    It would apear that the temp is not what it should be in the case and the comp is being flooded with liquid.
    If it is only one evap with one metering device I would look at that. It would appear that the valve has failed and is flooding liquid through.

    Another posibility is the defrost. If the evap is iced up it could flood back to the comp and if it is on hot gas defrost the defrost valve could be passing and putting just enough vapour through to cause the fault.

    1 look to your metering device.
    2 look at the evap for iceing up.
    3 look at your defrost in genral.

    Cheers taz.

  6. #6
    Join Date
    Jul 2006
    Location
    uk
    Age
    46
    Posts
    46
    Rep Power
    0

    Re: body-iced up(compressor

    are the fans running? is the evap iced up? is there a liquid line heat exchanger? i have had them split internally before now passing liquid into suction line. if you have a tev is the bulb still strapped to the suction line?

  7. #7
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: body-iced up(compressor

    Check the expansion valve bulb is clamped correctly, I had one on a freezer cold room where the previous engineer had clamped the bulb with plastic cable ties, the ties became brittle, snapped and left the bulb dangling, valve wide open, compressor a ball of ice.

  8. #8
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: body-iced up(compressor

    all of the above and maybe someone might have filled it with R22 instead, or if its a newish second hand set up,is the evap big enough for the unit,or just plain needing more defrosts.

  9. #9
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Thumbs up Re: body-iced up(compressor

    Everything is already mentioned by our friends . Please keep us posted what you found.
    Cheers
    Even Einstein Asked Questions