    Freezer efficiency questions



    I have a freezer running at (say) 0 deg. F with the compressor and condenser
    some distance away (about 80 ft.). As usual, the liquid line is not insulated and
    the suction line is. The refrigerant is R-409a, which has a heat of vaporization
    of about 95 BTU/pound, a specific heat of about 0.29 and 0.17 BTU/pound/deg. F
    for liquid and vapor, respectively.

    The liquid refrigerant leaves the condenser at (say) 90F, looses (say) 10F through the
    uninsulated liquid line and enters the evaporator at 80F where for each pound of
    refrigerant that evaporates, 95 BTU is absorbed. Of that, 23.2 BTU (80*.29) is used
    to cool the liquid refrigerant and the remaining 71.8 BTU is used to maintain the
    freezer at 0F.

    Am I mostly correct so far?

    The vaporized refrigerant leaves the evaporator at 0F (I am assuming the evaporator
    is an efficient heat exchanger), and despite the efforts of the insulation on the
    suction line, removes heat from the atmosphere and finally gets
    back to the compressor at (say) 60F.

    Question 1: Is it true that I am using almost 25% of my cooling on the specific heat
    of the refrigerant?

    Now, suppose I remove the insulation from that vapor return line, put the liquid and
    suction lines in good thermal contact, and put the insulation back around the whole
    mess so that I have a nice long heat exchanger. So the liquid will enter the evaporator
    cooler, permitting more of the heat of vaporization to cool my freezer, and the suction
    line will have a warmer average temperature so I won't be cooling the atmosphere
    as much.

    Let me assume that the liquid is cooled to 20F before entering the evaporator
    (because of the counter flow in our newly created heat exchanger, this should
    be possible?). Then, of that 95 BTU heat of vaporization for each pound,
    only 5.8 BTU are used in dealing with the specific heat of the liquid refrigerant
    and 89 BTU can be used to cool my freezer.

    Has my freezer just gotten 24% more efficient?
    What is wrong with this?
    Why is this not done when there is a large temperature difference condenser and
    evaporator temperature, as is the case with a freezer?



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Freezer efficiency questions

    In cap tube freezers, it is not uncommon to solder the cap tube to the suction line and this is sufficient heat exchange.

  3. #3
    Join Date
    Nov 2003
    Location
    NSW, Australia
    Age
    40
    Posts
    242
    Rep Power
    21

    Re: Freezer efficiency questions

    lots of freezer coils (depending on size) do have a heat exchanger located inside the room this is done by the same principal gary is explaining exept the liquid line passes through the suction line before heading to the tx valve in the coil.

    the more you can subcool your liquid before it gets to your metering device the more effective it will work this is correct.

    the exact gains made can be seen if you were to plot a ph diagram of the current cycle, then redo another once you have made your heat exchanger.
    "Old fridgies never die, they just run out of gas!"

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Freezer efficiency questions

    Now, suppose I remove the insulation from that vapor return line, put the liquid and
    suction lines in good thermal contact, and put the insulation back around the whole
    mess so that I have a nice long heat exchanger.
    If you are going to place suction line and liquid line "in good thermal contact", solder them together to increase thermal contact and avoid electrolysis.

  5. #5
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Freezer efficiency questions

    Quote Originally Posted by Gary View Post
    If you are going to place suction line and liquid line "in good thermal contact", solder them together to increase thermal contact and avoid electrolysis.

    I went to a freezer once that the condensing unit had been replaced on and two engineers couldn't get down in temperature, low suction, high head

    The unit was above the false celing and had a condenser fitted for the low temp range only. So I determined that the liquid line was a discharge line so the onlt thing to do was change the unit or help it get down to design conditions.

    So I stripped off the armaflex and cable tied the 3/8" liquid to the 7/8" suction and rearmaflexed the lines.

    The room came down no problem if it was up to me I would have changed the unit, but the commercial service manager was happy the customer was happy, so there was no problem

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Freezer efficiency questions

    Is there anyhow a saving?

    The heat of the liquid line is transported to the suction, so the mass flow and especially the temperature of the suction gasses will increase.
    What you save on one is lost again on the other side.
    Just throwing in this thoughts.

    You will have no flas gas at the metering device, that's for sure.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Freezer efficiency questions

    Quote Originally Posted by Peter_1 View Post
    Is there anyhow a saving?

    The heat of the liquid line is transported to the suction, so the mass flow and especially the temperature of the suction gasses will increase.
    What you save on one is lost again on the other side.
    Just throwing in this thoughts.

    You will have no flas gas at the metering device, that's for sure.
    There is only an energy savings if the evaporator consequently absorbs more heat due to its increased efficiency (increased active area). The heat exchanger, as you say, is a trade off.

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Freezer efficiency questions

    Agree Gary, so you must mount the bulb of the TEV after the HE which seems forbidden by all the HE manufacturers.
    You then haven't evaporator SH anymore.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Freezer efficiency questions

    Quote Originally Posted by Peter_1 View Post
    Agree Gary, so you must mount the bulb of the TEV after the HE which seems forbidden by all the HE manufacturers.
    You then haven't evaporator SH anymore.
    This can be gotten around by using two HE, with the bulb mounted in between them.