    prosab II Panel



    I have problem in prosab Panel with Sabroe screw compressor . We see error on screen (brine low temp. ) and the compressor does'nt run
    asking help Thanks



  2. #2
    Join Date
    Mar 2006
    Location
    Norfolk
    Posts
    160
    Rep Power
    19

    Re: prosab II Panel

    Not had experiance on that one but I would check the heater, the stat and trips or fuses.

    Paula

  3. #3
    Join Date
    Jun 2006
    Location
    Denmark
    Age
    55
    Posts
    15
    Rep Power
    0

    Re: prosab II Panel

    Hi.
    It seems that you have a broken PT100 sensor or that the connection/cabel is damaged.

    Is the Brinetemp showing fx.-200.

    HGS

  4. #4
    Join Date
    Mar 2007
    Location
    Egypt
    Age
    55
    Posts
    54
    Rep Power
    18

    Re: prosab II Panel

    Dears / Paulajayne and HGS
    Thanks for your interested and I'll Check all connection for all sensors
    Can you explain what is Brine temp?
    I know the Brine is Ca cl2 solution
    regards

  5. #5
    Join Date
    Mar 2006
    Location
    Norfolk
    Posts
    160
    Rep Power
    19

    Re: prosab II Panel

    Hi

    I think a translation problem here.

    "TEMP" is short for "Temperature"


    Paula