    EEVs



    Hi, wonder if anyone could give a little info on electronic expansion valves.

    What I have to do is build a unit from scratch, one compressor and two evaporator and would very much like to incorporate a pair of EEV.
    I been looking at danfoss system and have come to the conclusion that two akv10-1 and akc115a controller may just meet my needs.

    So saying that, what is the Danfoss setup like? reliable? easy to setup etc?? good points, bad points.....

    Also, I see Alco produce an eev system, anyinfo on Alco product?

    So many questions too little time
    Thanks in advance for any help



  2. #2
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    753
    Rep Power
    25

    Re: EEVs

    On a single liquid line feed the pulsing of the akv's can cause liquid hammer and hard to stabilise sst - better off on a large header fed system with multiple evaps. For a single system step motor valves provide much better operation and are availabe for use with a small danfoss ekc controller, carel do them too. Hope this helps.

  3. #3
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: EEVs

    Setup on the AKC controllers is a bit of a pain using the hand controller and can take a while to get the hang of. The Alco system with the stepper motor valves is more suitable for multiple evaporators as 750 Valve says that the AKV's tend to cause hammer in the liquid line which I have never managed to solve.

    Ian

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: EEVs

    My favourite is Polycool from siemens.
    https://www.hqs.sbt.siemens.com/oem/e/oem_ref_dow.asp

  5. #5
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: EEVs

    Quote Originally Posted by alpha View Post
    Hi, wonder if anyone could give a little info on electronic expansion valves.

    What I have to do is build a unit from scratch, one compressor and two evaporator and would very much like to incorporate a pair of EEV.
    I been looking at danfoss system and have come to the conclusion that two akv10-1 and akc115a controller may just meet my needs.

    So saying that, what is the Danfoss setup like? reliable? easy to setup etc?? good points, bad points.....

    Also, I see Alco produce an eev system, anyinfo on Alco product?

    So many questions too little time
    Thanks in advance for any help
    alpha

    The merits of EEVs in this application would be limited.
    If the system is not designed 100% correctly, it would have problems as mentioned previously.

    Regards

    Mark

  6. #6
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: EEVs

    Quote Originally Posted by Pooh View Post
    Setup on the AKC controllers is a bit of a pain using the hand controller and can take a while to get the hang of. The Alco system with the stepper motor valves is more suitable for multiple evaporators as 750 Valve says that the AKV's tend to cause hammer in the liquid line which I have never managed to solve.

    Ian
    Hi Guys

    we would fit danfoss on such an application. It would take me a matter of minutes to set up the AKC 115 controller.

    Having saidthat think about using a AK2 CC controller, this will eventually superceed the AK range.This type of controller in a bit like a PLC with inputs and outputs. You use a program called service tool set the contoller up once, then use a sofware download to each subsequent controller, it takes about 2 minutes to download an AK2 CC program once you have pre written the program for your set up.

    As for the valve pulsing effecting the liquid line and supply of liuid to the valve that is all down to the correct sizing of the liquid line, the correct velocity chosen and the amount of available subcool.

    In my experience pulse width valves are less troublesome than stepper motors that require battery drivers to shut them during a power failure. I have seen a few 100hp compressors burnt out due to the Carel version of the stepper motors on chillers manufactured in the UK (The Alco valve is a badged carel)

    Danfoss also produce an EKC 414 single evaporator controller, which is able to be set up from a dispaly (two needed in this case) no handheld and probably only a dozen parameters to set up.

    Danfoss also have a stepper motor expansion valve available, but only in large sizes, they can use the carel valve on some on there din mounted EKC range, (EKC 316 I think) if you want to go this route.

    We use Danfoss, I know Danfoss, the engineers know Danfoss, they have a large range and the product back up and relyability. I advise Danfoss

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  7. #7
    scruffy's Avatar
    scruffy Guest

    Re: EEVs

    Hello,
    I have had the experience of setting up EEV's on a similar system myself. I found using EEV's on a small system like this pointless. The controllers are not perfect. One evap may achieve its superheat and close the valve down. The suction pressure then drops and the superheat for the other evaporator then increases dramaticly and the valve opens. The other valve then re-opens, the valve that has opened up to compensate for the low suction pressure then doesn't close down fast enough and then the issue of floodback arrises. This valve with low superheat then closes down and the process starts over again. The best RMD for this system would be a simple TX valve. It would be cheaper, easier to install, more reliable and probably better on the warranty account. The only time i have seen an EEV work without causing trouble is on a system with 10 or more evaporators. If the customer wants the fridges to alarm on hi temp sell them a simple M2 alarm system from danfoss. Or even cheaper wire 2 revers acting thermostats in paralell with a buzzer.

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: EEVs

    For those like me with faithfulness in big manufacturers, like Siemens, here's an email just smoking in my mailbox (email addresses covered to protect the innocents). The argument here is CPS40 new EEV regulator and controller.

    ***** wrote:
    > Dear *****,
    >
    >
    > Regarding our alarm problem:
    > The alarming logic is wrong implemented.
    > We have to adapt the software. I will inform you as soon as I have the new version.
    >
    > Best regards,
    > *****

  9. #9
    Join Date
    Oct 2002
    Location
    Hampshire
    Posts
    156
    Rep Power
    22

    Re: EEVs

    Hi, thanks for the feedback all, much appreciated and of much help

    So you now got me thinking, should I really stick with what I know?, TEV.
    Yeah but no but.... I really want to play with EEV.
    The whole project (not intended for a customer but for my own use) is going to be used in electronics cooling, one evap for direct surface mount spot cooling and the other for ambient air, that's about all I can say for now on that unfortunately, apart from the heat loads will pretty much be non fluctuating, a consistent level load.

    Having said that, a TEV is kind of not favourable in this application because if I need to tweek superheat it's going to be a bit of a pain, switch off electronics, remove lid, tweak screw refit and try again, I do hope that EEV would allow me to tweak superheat to some degree on the fly as if to say..

    *back into deep thought mode.

  10. #10
    Join Date
    Jun 2004
    Location
    wales
    Age
    53
    Posts
    25
    Rep Power
    0

    Re: EEVs

    When we are on the subject of eev`s,i have two new denco units with carel eev`s on them and i am having murder try to set the superheat(denco no help)anyone else worked on these?Everything else is ok (head,liquid,sub cooling)just s/h

  11. #11
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: EEVs

    Quote Originally Posted by dai kin View Post
    When we are on the subject of eev`s,i have two new denco units with carel eev`s on them and i am having murder try to set the superheat(denco no help)anyone else worked on these?Everything else is ok (head,liquid,sub cooling)just s/h
    Superheat toolow or too high

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  12. #12
    Join Date
    Jun 2004
    Location
    wales
    Age
    53
    Posts
    25
    Rep Power
    0

    Re: EEVs

    Too high,but i think it is slightly short of r407c.Going back on monday when all the equipment is going on,so i will have some heat load and will be able to check it properly.(I have spent the last four years on vrv install and forgot all my fridge know-how)

  13. #13
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: EEVs

    Quote Originally Posted by Andy View Post
    Hi Guys

    we would fit danfoss on such an application. It would take me a matter of minutes to set up the AKC 115 controller.

    Having saidthat think about using a AK2 CC controller, this will eventually superceed the AK range.This type of controller in a bit like a PLC with inputs and outputs. You use a program called service tool set the contoller up once, then use a sofware download to each subsequent controller, it takes about 2 minutes to download an AK2 CC program once you have pre written the program for your set up.

    As for the valve pulsing effecting the liquid line and supply of liuid to the valve that is all down to the correct sizing of the liquid line, the correct velocity chosen and the amount of available subcool.

    In my experience pulse width valves are less troublesome than stepper motors that require battery drivers to shut them during a power failure. I have seen a few 100hp compressors burnt out due to the Carel version of the stepper motors on chillers manufactured in the UK (The Alco valve is a badged carel)

    Danfoss also produce an EKC 414 single evaporator controller, which is able to be set up from a dispaly (two needed in this case) no handheld and probably only a dozen parameters to set up.

    Danfoss also have a stepper motor expansion valve available, but only in large sizes, they can use the carel valve on some on there din mounted EKC range, (EKC 316 I think) if you want to go this route.

    We use Danfoss, I know Danfoss, the engineers know Danfoss, they have a large range and the product back up and relyability. I advise Danfoss

    Kind Regards Andy
    New job Andy

  14. #14
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: EEVs

    Quote Originally Posted by Andy View Post
    In my experience pulse width valves are less troublesome than stepper motors that require battery drivers to shut them during a power failure.
    That's how Carel is doing things.
    Siemens stepper motor controlled valves have a return spring.

  15. #15
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: EEVs

    Quote Originally Posted by NoNickName View Post
    That's how Carel is doing things.
    Siemens stepper motor controlled valves have a return spring.
    Hi NoNickName

    didn't know that, but it might explain why the airedale chillers have nice shinny stainless expansion valves on the newer models and they say the expansion valve problem has been fixed (must be a siemens valves with airedales name on it).

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  16. #16
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: EEVs

    Quote Originally Posted by MarkFiddy View Post
    New job Andy

    no I don't work for Danfoss, but I do like there electronic controllers and their inverter drives
    There industrial valves are over priced and they make a good maneurope pot compressor, but not really effecient enough for the market today

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  17. #17
    Join Date
    Aug 2006
    Location
    Scotland
    Posts
    104
    Rep Power
    18

    Re: EEVs

    Quote Originally Posted by dai kin View Post
    When we are on the subject of eev`s,i have two new denco units with carel eev`s on them and i am having murder try to set the superheat(denco no help)anyone else worked on these?Everything else is ok (head,liquid,sub cooling)just s/h
    Which refrigerant? To glide or not to glide?

    cheers

    Andy P

  18. #18
    Join Date
    Apr 2010
    Location
    Hudds
    Age
    50
    Posts
    75
    Rep Power
    15

    Re: EEVs

    Quote Originally Posted by dai kin View Post
    When we are on the subject of eev`s,i have two new denco units with carel eev`s on them and i am having murder try to set the superheat(denco no help)anyone else worked on these?Everything else is ok (head,liquid,sub cooling)just s/h
    Why do you want to set up the s/h ?? is the EEV set up correctly??

    Is it a EEV1 or a EEV2 ... how old is the unit?


    Talk to me and you may get the answer you are looking for.
    Rob Woodworth
    GEA Denco Technical Support
    rob.woodworth@geagroup.com

  19. #19
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: EEVs

    Quote Originally Posted by Denco Technical View Post


    Talk to me and you may get the answer you are looking for.

    .... er, this thread is some 4 years old, Rob!

    He might have sorted it by now!


    .

  20. #20
    Join Date
    Apr 2010
    Location
    Hudds
    Age
    50
    Posts
    75
    Rep Power
    15

    Re: EEVs

    lets hope so eh !!
    Rob Woodworth
    GEA Denco Technical Support
    rob.woodworth@geagroup.com

  21. #21
    batulao's Avatar
    batulao Guest

    Re: EEVs

    The new Electronic Expansion Valve from Carel, called EVD EVO (for evolution) is pretty amazing in terms of simplicity of configurations and auto adaptability:
    From a configuration point of view, you only need to setup 4 parameters (Refrigerat type, Valve size, Type of Sensors and Application on which the EEV is installed - Cabinet, cold room, chiller etc.). It's none!!!! The driver finds the most suitable parameters to operate with stability the system! This driver has also been enriched with ad Autotuning Algorithm which helps overcome any unbalanced system... Have a look at the video and datasheets at this link:
    http://www.i-acs.co.uk/store/index.p...vd0000e50.html

  22. #22
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: EEVs

    I would be quite careful before considering Carel. It's on a very steep downslope .