    Re: Connecting Trane Water chiller to air handling unit

    Hi Celtictech

    The use of a buffer tank on a chilled water circuit will smooth out the start / stop of the chiller providing the chiller is operating on return water control.

    The Binder points, usually installed either side of the orifice plate/valve, allow you to connect a manometer to measure the pressure drop across the orifice plate/valve. By plotting the dp on the valve chart you can adjust the flow rate to match the chiller requirement.

  2. #2
    Join Date
    Mar 2007
    Location
    Ireland
    Posts
    5
    Rep Power
    0

    Re: Connecting Trane Water chiller to air handling unit

    Hi,
    Thanks for the help , the chiller and equipment was purchased second hand so I've been told we have to use it , its probably not ideal having such a large chiller on a small load.